    Install VFD's on Package unit (newbe)



    Hi, I have a question? I can install a VFD on the blower of the roof top package Unit? If yes what do i do with the refrigerant? it will ice up the coil write?
    I heart that i can fix this installing a solenoid valves on the refrigerant lines and bypass the evaporator. This is thrue?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Install VFD's on Package unit (newbe)

    What is it that you are trying to acheive by fitting the VFD and why ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Sep 2009
    Location
    NYC
    Age
    39
    Posts
    9
    Rep Power
    0

    Re: Install VFD's on Package unit (newbe)

    Quote Originally Posted by 8lien View Post
    Hi, I have a question? I can install a VFD on the blower of the roof top package Unit? If yes what do i do with the refrigerant? it will ice up the coil write?
    I heart that i can fix this installing a solenoid valves on the refrigerant lines and bypass the evaporator. This is thrue?
    the only time i have seen a VFD used on the EVAP-blower is in VAV application, this is to maintain the static pressure in the duct and keep it from overpressurized the duck. as for installing a HOTGAS bypass, what is the point. You will be waisting energy.
    As you VFD ramps down you will have to cycle you compressors to keep the coil from freezing.

  4. #4
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    400
    Rep Power
    18

    Re: Install VFD's on Package unit (newbe)

    Rather have one on the compressor which can maintain a constant suction pressure . It will enhance compressor life & save you energ etc

  5. #5
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17

    Re: Install VFD's on Package unit (newbe)

    Packaged unit evaporator fan itself will be 1 to 3 HP depending on the size and VFD for such application is not economical.
    Even where VFD are used for compressors it is advantageous only when there is wide variation in wet bulb temperature for water cooled chillers.
    No doubt VFD will save energy but Life Cycle cost need to be assessed as Operation cost alone is to the tune of 55 to 65%.Logically for higher size motors say multiple AHU's having VFD will save lot of energy.

  6. #6
    8lien's Avatar
    8lien Guest

    Re: Install VFD's on Package unit (newbe)

    Thanks for the fast response if I have another question I will ask you guys.

Similar Threads

  1. Daikin a/c units.
    By rick in forum Air Conditioning
    Replies: 59
    Last Post: 18-02-2008, 10:22 PM
  2. Problem with ducted Daikin
    By jutty in forum Trouble Shooting
    Replies: 8
    Last Post: 23-07-2007, 05:34 AM
  3. Help with a dreaded LG unit..
    By marc5180 in forum Air Conditioning
    Replies: 18
    Last Post: 17-03-2007, 10:24 PM
  4. Replies: 8
    Last Post: 16-06-2006, 01:55 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •