    pipe installation



    Hi,

    I have been asked to install some coldroom pipes on cable tray, seeing as the liquid pipe is not lagged, can anyone see a problem with this?

    It will help with protection as its on a mezzanine floor where people can walk over them.

    I have done this before and cable tied discharge and liquid lines from a close control unit directly to a cable tray. Yes it did look s***.

    How do you all do it?



  2. #2
    Join Date
    Jul 2009
    Location
    South Africa
    Age
    79
    Posts
    195
    Rep Power
    17

    Re: pipe installation

    I would not strap a copper pipe to a steel tray without a plastic standoff clip. Different metals hard together can cause fast corrosion.

  3. #3
    Join Date
    May 2009
    Location
    uk
    Age
    62
    Posts
    44
    Rep Power
    0

    Re: pipe installation

    insulate liquid line and tie wrap both together

  4. #4
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: pipe installation

    Cant see any problem at all, just cable tie the liquid to the insulated suction -it's how it's been done for years and years-If price allows insulate them both

    I have never heard of a problem with a copper pipe on a cable tray causing some electrolysiscorrosion-Perhaps Frikkie can show us actual examples?

    However if there is a chance of people treading on it then for protection, you should double up the tray to make a tray/pipe sandwich

  5. #5
    Join Date
    Jul 2009
    Location
    South Africa
    Age
    79
    Posts
    195
    Rep Power
    17

    Re: pipe installation

    Quote Originally Posted by multisync View Post
    Cant see any problem at all, just cable tie the liquid to the insulated suction -it's how it's been done for years and years-If price allows insulate them both

    I have never heard of a problem with a copper pipe on a cable tray causing some electrolysiscorrosion-Perhaps Frikkie can show us actual examples?

    However if there is a chance of people treading on it then for protection, you should double up the tray to make a tray/pipe sandwich
    Hello Multisync,

    I don't have any pictures of corrosion but electrical regulation in many areas forbid laying bare copper earthing wires in tray without insulation. Corrosion is moisture related.
    Quote.
    A bare copper equipment grounding conductor should not be placed in an aluminum cable tray
    due to the potential for electrolytic corrosion of the aluminum cable tray in a moist environment.
    For such installations, it is best to use an insulated conductor and to remove the insulation where
    bonding connections are made to the cable tray, raceways, equipment enclosures, etc.
    Source here
    Aluminum is worse than steel but any different metals in contact will corrode.

  6. #6
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: pipe installation

    your better off to install suction line so as no compression of pipe insulation occurs,i prefer to tape the liquid line,if compression is a problem use insulation with a larger wall thickness
    mmm to beer or not to beer...........lets drink breakfast

  7. #7
    Join Date
    Feb 2008
    Location
    manchester
    Posts
    80
    Rep Power
    17

    Re: pipe installation

    put the liguid line behind the insulated suction pipe. 6inch of armaflex tape wrapped round both pipes then cable tie to tray. The tape will stop the cable tie cutting into the insulation

  8. #8
    Join Date
    May 2008
    Location
    UK
    Posts
    170
    Rep Power
    16

    Re: pipe installation

    Thanks guys,

    If the liquid line is insulated will this effect the subcooling?

    In superstores we lay pipes on unistrut with Armaload glued to it. We tape the pipes to each other with Armaflex tape. I suppose you could put a small section of insulation, say 50mm, around the pipe where each cable tie is.

Similar Threads

  1. refrigerant pipe installation practice
    By jedax81 in forum Industrial
    Replies: 11
    Last Post: 29-10-2010, 04:17 AM
  2. The pipe of the split A/C installation
    By James priyono in forum Air Conditioning
    Replies: 5
    Last Post: 18-06-2009, 11:33 PM
  3. Pipe Installation
    By Rodders in forum Air Conditioning
    Replies: 5
    Last Post: 08-06-2009, 12:37 AM
  4. Mitsubishi PUHZ-RP200YHA Pipe Sizes
    By gwilliamson in forum Air Conditioning
    Replies: 11
    Last Post: 14-05-2008, 09:43 PM
  5. Copper pipe joint Installation Question
    By drew71 in forum Technical Discussions
    Replies: 8
    Last Post: 14-01-2008, 12:57 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •