    mitsubishi vrf
    office building with 4 indenticle systems.4 units to each system using splitter/branch pipework.perfect pressures when heating but when cooling pressures 3b low and 10b high using r407. measured pipework and charge is correct.al systems operating the same way.outdoor freezing when cooling.
    Split Croatia
    57
    6,151
    36
    Re: mitsubishi vrf
    Check systems separately.
    Jul 2009
    ireland
    38
    Re: mitsubishi vrf
    systems WHERE all checked seperately and running at the same low pressures
    Jul 2009
    Berkshire
    175
    15
    Re: mitsubishi vrf
    I know Mitsubishi kit, like other VRF systems, will try to maintain a suction pressure that gives you an evaporating temperature of just above 0 degrees celsius. 10 bar is pretty much the minimum head pressure you would want in cooling mode.
    I find it strange all 4 would be playing up .... or you're very unlucky!
    Start by comparing your pressure gauge readings with what the outdoor unit thinks the pressures are; via dip switch settings on SW1.
    Silly questions too: is there enough heat load in the building? Are you running all 4 indoor units at the same time when reading those pressures? Are the evaporators clean and clear? Any fault codes?
    If at first you DO succeed, try to hide your astonishment!!
    Mar 2007
    Warwickshire UK
    723
    21
    Re: mitsubishi vrf
    The outdoor unit PUHY --- YMF-C ?
    Outdoor unit suction accumulator a block of ice ?
    The older Y series did tend to run at low discharge pressure anyway
    but
    3 bar suction
    The unit has target evap temp of arround 0 so would expect suction around 4.5 to 5.5 bar.
    It controls on the TH2 suction temp data.
    So make sure the TH2 has correct temperature data at the outdoor unit display with SW1 setting.
    For example if the TH2 sensor is reading 10 deg C high then the compressor will remain at high speed & overshoot on the suction pressure.
    So when the suction temp is below 0 the compressor will start ramping down & thats why you will have poor discharge pressure.
    You need to find out why the suction pressure is so poor.
    As its a Y system the prime suspect is the LEV valves at the indoor units locked or blocked strainers.
    If the system is operating in computer room application with lower than 15 deg C WB return air then you might get this type of poor performance as the system is operating outside its design limits.
    In this case you would need to deploy some extra head pressure control to force the outdoor unit to run at higher discharge pressure provided no other problem with the system.
    Please come back with mode details
    Split Croatia
    57
    6,151
    36
    Re: mitsubishi vrf
    Is that system just commissioned and you conducting start up?
    Or that system is alreedy worked OK and now it plays up?
    Jul 2009
    ireland
    38
    Re: mitsubishi vrf
    found the problem 2 b that the outdoor / coil was oversized and was freezing up.the new models from mitsu have a split coil which have a solonoid valve that lets you use more of the coil when needed.we blocked the back coil wit cardboard and both pressures shot up to 3.8low and 17.4high.going to use a kontacter and pressure swith to delay the fan until pressure reachs about 19bar and that should balance the system. cheers
    Split Croatia
    57
    6,151
    36
    Re: mitsubishi vrf
    Quote Originally Posted by morgan c View Post
    Outdoor coil in cooling mode act as condenser and with your reported pressure of 10 bar (r 407C = 22°C/28°C) it cannot freeze even in theory.
    Second, Mitsubishi have condensation control and could cool without problem (and control condensation pressure) even when outdoor temperature is below 0°C.
    You should revise your writing here because it doesn't make any sense.
    Mar 2007
    Warwickshire UK
    723
    21
    Re: mitsubishi vrf
    The contactor & pressure switch will work ok to stop overcondensing.
    When setting up the pressure switch monitor the TH2 temp sensor of the indoor units at the outdoor circuit board using the SW1.
    Increase the HP until you get the indoor units running at more than 1 deg C on the TH2.
    Any lower than 1 deg C & the indoor units stop every 5 mins on coil frost prevention so if you can pull the suction temp up so the coil temp at the TH2 sensor is above coil frost prevention temp the indoor units will continue to cool untill room temp down to set temp.
    Apr 2009
    israel
    778
    Re: mitsubishi vrf
    HI THERE "The contactor & pressure switch will work ok to stop overcondensing"
    this makes no sense the mitsu units work great till -10 c with no pressure switch aded!!
    unless someone oversized the entire system and even then !!
    i could not understand what u described here 145 psi is way above 0 deg c so how is there ice on the condenser ??
    what is your outside temp?
    Split Croatia
    57
    6,151
    36
    Re: mitsubishi vrf
    Quote Originally Posted by goshen View Post
    It looks that they are speaking some secret language. I think, same as you, that what is described in these few posts by Morgan doesn't make any sense if interpreted as written.
    And I am not god in mind reading to know what is meant and not written.
    I could only guess ( as Thermatech did) that this system is used as cooling system in some server room with low humidity where it is not suppose to be, because it is not designed for that, and OP mean that INDOOR units are freezing (but nowhere in his text he said that)!
    Jul 2009
    ireland
    38
    Re: mitsubishi vrf
    sorry guys i just got mixed up the outdoor was freezing at the suction and out on to the accumalater bcause of the low bk pressure.the outdoor unit was oversized causing the over condensing.thanks 4 all the posts and advice(thermatech).
  1. mitsubishi electric v mitsubishi heavy ind
    By coolhibby1875 in forum Air Conditioning
    Last Post: 04-09-2009, 01:42 PM
  2. Few question about Mitsubishi Heavy Industrial air condition
    By fireduck in forum Air Conditioning
    Last Post: 12-05-2009, 02:35 PM
  3. [Ask] Mitsubishi rotary compressor
    By felixfab_93 in forum Refrigeration Books
    Last Post: 18-12-2008, 10:48 AM
  4. Mitsubishi Light Truck Refrigeration
    By Mastercool in forum Transport
    Last Post: 23-11-2007, 06:15 AM
  5. Mitsubishi compressor lock
    By marc5180 in forum Air Conditioning
    Last Post: 08-10-2007, 05:48 PM