    trane rthb oil



    hi we have a rthb380 unit that works well ,but under extreme conditions ,condesning water supply is 34 deg c ,pressure drop on both evap and condenser are as desigend, unit operates all summer at 100% capacity ,their is no odd noise from compressor ,the unit is charged with r-22 ,
    recently oil chekup came back with 95 ppm of copper, all other parameters are ok, no metal or oxidation ,
    the unit uses oil025e, we suspect the bearings in the comp or errosion in pipes.
    anybody encounter this problem ???
    we are going to change all the oil and filter,
    any ideas???
    Last edited by goshen; 25-09-2009 at 12:06 PM.



  2. #2
    Join Date
    Dec 2008
    Location
    UK
    Posts
    55
    Rep Power
    16

    Re: trane rthb oil

    Hi Goshen, How is the hours/starts ratio?? Also If this is still the original oil filter and oil I have found quite a lot of "Manufacturing Debris" in the first filter. Have you changed the liquid line refrigerant filter. In most cases the whole charge needs to be removed but on some of these machines they had isolation valves to enable a pump down. With these large screws if the bearings were "shot" you would have metal particles in suspension in the sample analysis. I have also found metal flakes in the filter housing when the bearings are worn. However, as you say that the machine runs fully loaded most of the time I`m fairly confident that an oil and filter change will effect a positive outcome.Good luck!!

Similar Threads

  1. AEC Pinical chiller with trane comp
    By cptrdbrd in forum Commercial
    Replies: 1
    Last Post: 28-10-2009, 09:47 PM
  2. trane ertaa213 EEV fault (1AA)
    By knight rider in forum Technical Discussions
    Replies: 4
    Last Post: 11-06-2009, 06:40 AM
  3. New to Forum, Facing problems related with TRANE Chiller
    By neerajpuranik in forum Air Conditioning
    Replies: 3
    Last Post: 10-12-2008, 02:43 AM
  4. Trane CVHE 450 R11 Centrifugal Chiller
    By albertjoseph in forum Air Conditioning
    Replies: 4
    Last Post: 06-10-2008, 03:23 PM
  5. Trane Defrost Control Board Energize "W" in cooling
    By jcmorris2 in forum Heat Pumps
    Replies: 6
    Last Post: 02-06-2007, 03:40 AM

Posting Permissions