Results 1 to 2 of 2
    xact's Avatar
    xact Guest
    dehumidification
    I am looking for some prety basic info about mechanical dehumidification by liquid cooled coils.
    I guess what I am after is how do I achive the greatest amount of dehumidification in a unit that has a fresh air/recerc damper/preheat coil/cooling coil and reheat coil.
    My train of thought is to bring the cooling as low as possible while reheating the air to a set temprature. My problem I think is the return air is around 60 and the cooling coil is only able to reach 43F in and around 55F out.
    Is it correct to assum I would only be able to achive a maximum RH of around 50%?
    any thoughts
    Mar 2009
    U.S.A.
    320
    Re: dehumidification
    That would be a minimum RH and a 33-deg Metal Temperature (evap tubes) on a 45 Deg Outlet Air Temperature from the cooling Coil will be just under 50% Relative Humidity....And the same air reheated REHEATED to 52 Deg Supply will be at about 40% RH.
    To get to what you room space will be like: You will need some means of developing the rate at which moisture will be added back to that 40% RH Air. I If there's a lot more moisture source than there are "dry" heat source, your reheat arrangement won't be very efffective; the room humidity will remain high.
  1. Large Air handling Equipment Dehumidification / Litres Per Hour ?
    By deluxairhead in forum Technical Discussions
    Last Post: 17-08-2009, 06:48 PM
  2. Bryant geothermal heat pump dehumidfier
    By Backhertz in forum New Technologies
    Last Post: 16-03-2008, 02:44 AM
  3. Dehumidification with VRF
    By mchild in forum Air Conditioning
    Last Post: 07-02-2008, 08:27 AM
  4. dehumidification
    By chillyblue in forum Fundamentals
    Last Post: 01-11-2007, 10:37 AM
  5. Dehumidification with a liquid desiccant.
    By Gelante in forum New Technologies
    Last Post: 16-09-2004, 10:22 PM