I am looking for some prety basic info about mechanical dehumidification by liquid cooled coils.
I guess what I am after is how do I achive the greatest amount of dehumidification in a unit that has a fresh air/recerc damper/preheat coil/cooling coil and reheat coil.
My train of thought is to bring the cooling as low as possible while reheating the air to a set temprature. My problem I think is the return air is around 60 and the cooling coil is only able to reach 43F in and around 55F out.
Is it correct to assum I would only be able to achive a maximum RH of around 50%?
any thoughts
-
01-10-2009, 02:22 AM #2
Re: dehumidification
That would be a minimum RH and a 33-deg Metal Temperature (evap tubes) on a 45 Deg Outlet Air Temperature from the cooling Coil will be just under 50% Relative Humidity....And the same air reheated REHEATED to 52 Deg Supply will be at about 40% RH.
To get to what you room space will be like: You will need some means of developing the rate at which moisture will be added back to that 40% RH Air. I If there's a lot more moisture source than there are "dry" heat source, your reheat arrangement won't be very efffective; the room humidity will remain high.
Similar Threads
-
Large Air handling Equipment Dehumidification / Litres Per Hour ?
By deluxairhead in forum Technical DiscussionsReplies: 12Last Post: 17-08-2009, 06:48 PM -
Bryant geothermal heat pump dehumidfier
By Backhertz in forum New TechnologiesReplies: 0Last Post: 16-03-2008, 02:44 AM -
Dehumidification with VRF
By mchild in forum Air ConditioningReplies: 3Last Post: 07-02-2008, 08:27 AM -
dehumidification
By chillyblue in forum FundamentalsReplies: 3Last Post: 01-11-2007, 10:37 AM -
Dehumidification with a liquid desiccant.
By Gelante in forum New TechnologiesReplies: 6Last Post: 16-09-2004, 10:22 PM