Over Condesing under condensing
Hello all
Can anyone help, I'm still new to all this and some of you veterans my find this a bit of a silly question ? Basically can a blocked condenser cause under condensing which in turn may cause a liquid line sight glass to flash ? I know a sight glass should have a full column of liquid but if the condenser is under condensing surely it is not producing this ? or do I need to rethink all the things I have learned about refrigeration. Basically can some one explain over condensing, under condensing or point me in the direction of a good book that may explain it
-
24-09-2009, 01:40 PM #2
Re: Over Condesing under condensing
By Under condensing I assume you mean not enough condensing.
In which case the answer is yes.
A blocked condenser will reduce the efficiency, so the hot refrigerant vapour will not all turn to liquid and therefor it will bubble down the liquid line.
If the cond is clean and efficient then the vapour will all change to liquid and then subcool a few degrees, resulting in a full liquid line and no bubbles.
It is hard to over condense for the most part because you can only cool down to ambient temps. If it is in the middle of winter and the condenser is on the roof with the wind and rain blowing through it you can over condense and the result would be very subcooled liquid and a drop in head pressure.
taz.Last edited by taz24; 24-09-2009 at 01:43 PM.
-
24-09-2009, 10:15 PM #3
Re: Over Condesing under condensing
Under condensing, as TAZ stated,
Over condensing, really does not occur, what this normally means is that your condensing pressure (thus liquid pressure) is to low to drive the correct amount of liquid through the expansion device, causing a low suction pressure. In some cases liquid can pool in the condensor (ome times known as "held up", giving the effect that the system is short of gas. In other words the reciever is not holding the liquid, so liquid and vapor enter the liquid line. Sub-cooling as and where that happens thats another thread!
-
24-09-2009, 10:38 PM #4
Re: Over Condesing under condensing
Thank you, that realy makes sense
Similar Threads
-
Over condensing under condensing
By jaymax in forum New to REReplies: 3Last Post: 25-09-2009, 08:08 AM -
High discharge temp
By paul_h in forum Air ConditioningReplies: 48Last Post: 06-05-2009, 11:10 AM -
condensing unit selection?
By ibraheem in forum Technical SpeculationsReplies: 0Last Post: 28-05-2008, 06:06 PM -
Condensing temp in refrigeration
By anup in forum FundamentalsReplies: 1Last Post: 02-10-2005, 11:18 AM