    Smile Over Condesing under condensing



    Hello all

    Can anyone help, I'm still new to all this and some of you veterans my find this a bit of a silly question ? Basically can a blocked condenser cause under condensing which in turn may cause a liquid line sight glass to flash ? I know a sight glass should have a full column of liquid but if the condenser is under condensing surely it is not producing this ? or do I need to rethink all the things I have learned about refrigeration. Basically can some one explain over condensing, under condensing or point me in the direction of a good book that may explain it



  2. #2
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Over Condesing under condensing

    Quote Originally Posted by jaymax View Post
    Hello all

    Can anyone help, I'm still new to all this and some of you veterans my find this a bit of a silly question ? Basically can a blocked condenser cause under condensing which in turn may cause a liquid line sight glass to flash ? I know a sight glass should have a full column of liquid but if the condenser is under condensing surely it is not producing this ? or do I need to rethink all the things I have learned about refrigeration. Basically can some one explain over condensing, under condensing or point me in the direction of a good book that may explain it

    By Under condensing I assume you mean not enough condensing.

    In which case the answer is yes.

    A blocked condenser will reduce the efficiency, so the hot refrigerant vapour will not all turn to liquid and therefor it will bubble down the liquid line.

    If the cond is clean and efficient then the vapour will all change to liquid and then subcool a few degrees, resulting in a full liquid line and no bubbles.

    It is hard to over condense for the most part because you can only cool down to ambient temps. If it is in the middle of winter and the condenser is on the roof with the wind and rain blowing through it you can over condense and the result would be very subcooled liquid and a drop in head pressure.


    taz.
    Last edited by taz24; 24-09-2009 at 01:43 PM.

  3. #3
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Over Condesing under condensing

    Under condensing, as TAZ stated,
    Over condensing, really does not occur, what this normally means is that your condensing pressure (thus liquid pressure) is to low to drive the correct amount of liquid through the expansion device, causing a low suction pressure. In some cases liquid can pool in the condensor (ome times known as "held up", giving the effect that the system is short of gas. In other words the reciever is not holding the liquid, so liquid and vapor enter the liquid line. Sub-cooling as and where that happens thats another thread!

  4. #4
    jaymax's Avatar
    jaymax Guest

    Re: Over Condesing under condensing

    Thank you, that realy makes sense

Similar Threads

  1. Over condensing under condensing
    By jaymax in forum New to RE
    Replies: 3
    Last Post: 25-09-2009, 08:08 AM
  2. High discharge temp
    By paul_h in forum Air Conditioning
    Replies: 48
    Last Post: 06-05-2009, 11:10 AM
  3. condensing unit selection?
    By ibraheem in forum Technical Speculations
    Replies: 0
    Last Post: 28-05-2008, 06:06 PM
  4. Condensing temp in refrigeration
    By anup in forum Fundamentals
    Replies: 1
    Last Post: 02-10-2005, 11:18 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •