    Aspen Mini Lime and Daikin FTX G series



    Hi Guys,

    I have never had to install a condensate pump before and I am a little confused what the best method of wiring an Aspen Mini Lime pump to a Daikin FTX G series unit is?

    Typically all the units have a rotary switch on the outside supplying the outside unit from which a 4 core SY supplies the inside unit through the 1 2 3 and G on the terminal block. I believe 1 = L 2 = N and 3 = Communication.

    Hope someone can help.

    Take care



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Aspen Mini Lime and Daikin FTX G series

    You could pick up a fused feed from the 1/2 indoor unit terminals. Most pumps are low current so do not affect the overall power layout.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Sep 2008
    Location
    England
    Posts
    18
    Rep Power
    0

    Re: Aspen Mini Lime and Daikin FTX G series

    cheers Brian, but what about the alarm side utilising the normally closed, normally open and common wires?

  4. #4
    Join Date
    Sep 2008
    Location
    England
    Posts
    18
    Rep Power
    0

    Re: Aspen Mini Lime and Daikin FTX G series

    Its OK one of my friends said they normally connect the common from the pump to no.3 of the cable coming from the outdoor unit to the indoor and the NC to terminal 3 of the indoor unit

    Thanks anyways

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Aspen Mini Lime and Daikin FTX G series

    If you read the wiring diagram in the pump box, you will see that Aspen recommend that the live to the indoor fan coil is wired through the high level float (NC) wires. In the event of a high level alarm, the power is removed from the indoor unit, instead of interupting the comms which will cause a fault to be generated (U4)

  6. #6
    Join Date
    Sep 2008
    Location
    england
    Posts
    427
    Rep Power
    20

    Re: Aspen Mini Lime and Daikin FTX G series

    Whenever I`ve fitted them I`ve always used a seperate supply via a fused spur as the instructions say using the indoor unit supply can cause problems. I don`t really see how this could happen but I`d rather be safe than sorry. A lot easier to fit a supply on the original install than when the shop, office etc is up and running. Plus the customer won`t pay you twice.

    Glenn

  7. #7
    Join Date
    May 2008
    Location
    UK
    Posts
    170
    Rep Power
    16

    Re: Aspen Mini Lime and Daikin FTX G series

    If you read the wiring diagram in the pump box, you will see that Aspen recommend that the live to the indoor fan coil is wired through the high level float (NC) wires. In the event of a high level alarm, the power is removed from the indoor unit, instead of interupting the comms which will cause a fault to be generated (U4)
    If you do this then it may be best to take the pump's power from the isolator before the unit and not the unit's power or you will switch the pump off on high level and it won't come back on. That's how I do it anyway.