Hi Guys,
I have never had to install a condensate pump before and I am a little confused what the best method of wiring an Aspen Mini Lime pump to a Daikin FTX G series unit is?
Typically all the units have a rotary switch on the outside supplying the outside unit from which a 4 core SY supplies the inside unit through the 1 2 3 and G on the terminal block. I believe 1 = L 2 = N and 3 = Communication.
Hope someone can help.
Take care
-
22-09-2009, 11:39 PM #2
Re: Aspen Mini Lime and Daikin FTX G series
You could pick up a fused feed from the 1/2 indoor unit terminals. Most pumps are low current so do not affect the overall power layout.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
23-09-2009, 07:22 AM #3
Re: Aspen Mini Lime and Daikin FTX G series
cheers Brian, but what about the alarm side utilising the normally closed, normally open and common wires?
-
23-09-2009, 08:21 AM #4
Re: Aspen Mini Lime and Daikin FTX G series
Its OK one of my friends said they normally connect the common from the pump to no.3 of the cable coming from the outdoor unit to the indoor and the NC to terminal 3 of the indoor unit
Thanks anyways
-
23-09-2009, 08:55 AM #5
Re: Aspen Mini Lime and Daikin FTX G series
If you read the wiring diagram in the pump box, you will see that Aspen recommend that the live to the indoor fan coil is wired through the high level float (NC) wires. In the event of a high level alarm, the power is removed from the indoor unit, instead of interupting the comms which will cause a fault to be generated (U4)
-
23-09-2009, 05:50 PM #6
Re: Aspen Mini Lime and Daikin FTX G series
Whenever I`ve fitted them I`ve always used a seperate supply via a fused spur as the instructions say using the indoor unit supply can cause problems. I don`t really see how this could happen but I`d rather be safe than sorry. A lot easier to fit a supply on the original install than when the shop, office etc is up and running. Plus the customer won`t pay you twice.
Glenn
-
23-09-2009, 08:05 PM #7
Re: Aspen Mini Lime and Daikin FTX G series
If you read the wiring diagram in the pump box, you will see that Aspen recommend that the live to the indoor fan coil is wired through the high level float (NC) wires. In the event of a high level alarm, the power is removed from the indoor unit, instead of interupting the comms which will cause a fault to be generated (U4)