    Hi first timer
    I HAVE A REBUILT 6 CYLINDER COPELAND ON A CHILLER ,WITH CLEVAS 32 OIL IN IT ON R22 THE OIL LEAVES THE COMP WITHIN 5MINS & GOE'S OFF ON OIL PRESSURE SWITCH ONLY 1/2 A BAR OIL PRESSUIRE. HAS IT HAD THE WRONG OIL PUT IN IT

    YOURS
    BOB2+1



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: synthetic oils

    Hi Bob and welcome to the forum!

    Basically clevas 32 may or may not be to thin.
    I am more used to seeing Clavus 68 with R22.
    Maybe some of the other Guys could advise on that?
    Basically of you read the data via the link below that I have attached.
    You will note that the oil diff can be set as low as 9psi.
    With apparently oil pressures near to that being acceptable.
    Anyway have a read and let us know what you think?
    Grizzly
    http://www.mediafire.com/?t01dbjyb9oy
    Last edited by Grizzly; 22-09-2009 at 04:18 AM.

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: synthetic oils

    Hi Bob,
    A common mistake among RE's is that oil just leaves the compressor.
    The common problem is oil return to the compressor.

    Oil circulate all the time in the system.

    My thought is that liquid refrigerant from the chiller washed the oil out of the compressor and it is in the chiller.
    In that case, I run the compressor with a little oil and let bring the oil back in normal working order.
    If it doesn't return, than there is a problem that need to be looked after and be solved.

    It has nothing to do with the type of oil.

  4. #4
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: synthetic oils

    I agree with all the above comments, but would add that I would look at oil separator if it has one, and actual suction temp entering compressor for saturation, oil pump regulator, sump heaters and oil temps. Oil viscosity would consider manufactures specification would probably 68., like Suniso 4Gs for R22.
    magoo

  5. #5
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: synthetic oils

    hi did you rebuilt the compressor or is it from a reman place,because if the compressor is pumping its oil out with in 5 minutes ,its bores are worn or the main bearing bearings are worn heavily because the oil pump is pumping the oil through the crank and straight into the winding section from there its going into the bores and out

  6. #6
    Join Date
    Aug 2009
    Location
    Turhona.libya
    Posts
    79
    Rep Power
    15

    Re: synthetic oils

    Compressor's crankcase should be kept warm during off cycle. If liquid refrigeran stayed in the compressor or liquid refrigerant is returned through suction port . This would dilute the oil and cause marginal lubrication and also allow most of the oil to leave the compressor, and would have to go through the complete system to get back to the compressor crankcase.

  7. #7
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: synthetic oils

    If I read this correctly, the compressor starts and the oil disappears from the sight glass and the LOC cuts out.

    Does the oil return after the compressor shuts down?

    If so, you may have a pressurized crank which causes "blow by". This results from the compressor running hot, breaking down the oil and wearing out the internal components. The worn cylinder walls then bypass gas which pressurizes the crank due to the internal check valve between the crank and motor compartment closing. After it sits idle the check valve opens and the oil returns.

    There is another valve in the crank called the Crankcase Ventilation Valve. When the crank is pressurized this valve opens to the suction chamber to relieve the pressure.

    In a "blow by" situation the excess pressure built up in the crankcase may exceed the ability of the crankcase ventilating valve to vent the crankcase causing the check valve to close.

    The oil pump is still picking up oil in the crank and pumping it through a drilled crank where it exits into the motor compartment.

    Measure the crank pressure and the suction pressure and if there is a pressure difference of 2 lbs or more then this is your problem.

    Replacing the compressor is the only solution if you have a worn compressor. Then you must find the reason for the overheating or it will happen again.

    Here is a picture that might help.
    Attached Images Attached Images
    Last edited by powell; 22-09-2009 at 03:31 PM.
    Thousands of HVACR manufacturers links! Visit: www.hvacrinfo.com

Similar Threads

  1. Replies: 4
    Last Post: 07-03-2010, 02:15 AM
  2. Refrigerant oils
    By Andrew F. in forum Fundamentals
    Replies: 4
    Last Post: 25-11-2009, 02:03 PM
  3. Refrigeration Oils
    By gwapa in forum NH3
    Replies: 10
    Last Post: 29-10-2009, 08:41 PM
  4. Refrigeration oils
    By johnemar in forum Refrigerants
    Replies: 2
    Last Post: 25-02-2003, 07:36 AM
  5. R-22 with ester oils
    By Friobernal in forum Technical Discussions
    Replies: 7
    Last Post: 24-05-2002, 05:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •