Results 1 to 17 of 17
    Mar 2009
    KZN, South Africa
    64
    2,212
    High superheat TXV
    A conventional adjustable TXV, for example Alco brand, will allow a maximum superheat setting of around 10.8-11.35K, at evaporator discharge.
    I am searching for an adjustable TXV which will allow stable control at superheats higher than this, perhaps as high as up to 14-15K.
    The intention is not to use a suction-line heater for this application.
    If there are alternative control-valve/sensors that will allow these high superheats to be reached, then I'd be interested as well.
    Auckland
    74
    3,357
    38
    Re: High superheat TXV
    Hi DesA
    have looked at using an Air conditioning rated TX valve, that operate at a higher superheat range. Sporlan do a CP100 txv cap.
    magoo
    Mar 2009
    KZN, South Africa
    64
    2,212
    Thanks so much Magoo. I'll follow up on the Sporlan CP100 TXV - much obliged.
    (I've tried adding to your reputation, but it tells me to keep spreading it around first
    Oct 2003
    5,630
    34
    Perhaps an electronic EEV like the E2V of Carel, not that expensive.
    Mar 2009
    KZN, South Africa
    64
    2,212
    Thanks very much Peter_1 - that's a good lead. Many thanks.
    Aug 2007
    42
    135
    Danfoss ETS and controller we have controlled superheat at 25'c
    The Bridge Keeper
    'Answer me these questions three, n'er the other side ye see.'
    What is your name?
    What is your favourite colour?
    What is your suction superheat?
    Oct 2003
    5,630
    34
    You're right about the Danfoss but compare once the price for both?
    Mar 2009
    KZN, South Africa
    64
    2,212
    Quote Originally Posted by HallsEngineer View Post
    Thanks very much, HE.
    Will check prices of all options over here.
    Mar 2009
    KZN, South Africa
    64
    2,212
    Hi DesA
    magoo
    What is the maximum SH the Sporlan CP100 TXV can be pushed to?
    Mar 2009
    KZN, South Africa
    64
    2,212
    Are there any other non-electronic TXV's with extended super-heat capability?
    Are for instance, stronger springs a possibility, for instance, for the Alco, Danfoss, Sporlan series TXV's?
    Would alternative bulbs be of use? The refrigerant in use is R-134a.
    Apr 2001
    79
    5,071
    35
    Quote Originally Posted by desA View Post
    I am curious as to why you would want higher superheat as this would reduce the mass flow and cause the compressor to run hotter?
    Apr 2001
    79
    5,071
    35
    You might consider switching to an AEV, set the Te,sat where you want it, then control superheat with fan speed. The higher the fan speed/heat load, the higher the superheat.
    Mar 2009
    KZN, South Africa
    64
    2,212
    There is method to my madness - the Magoo SH rule.
    Most conventional TXV's, cannot supply enough superheat to reach the Magoo-rule requirements.
    At this point, the additional superheat penalty is not a concern & the compressor power is not affected.
    Mar 2009
    KZN, South Africa
    64
    2,212
    That's a very useful thought - thanks for that. Mmhh...
    So, the AEV controls the Te,sat using mass-flow to maintain pressure. The fan speed adjusts heat input & hence superheat. Ok?
    Mar 2009
    KZN, South Africa
    64
    2,212
    A TXV with MOP - revisited:
    Can we review exactly how this works?
    Acts as a normal TXV until a certain limiting pressure (determined by MOP setting) has been reached, then TXV begins shutting back mass-flow & allows the superheat to drift upwards, in the process.
    Apr 2001
    79
    5,071
    35
    Mmmmm... not quite right. When the bulb pressure reaches its limit it cannot open the valve further, thus cannot increase the mass flow further. If the heat load then increases further, the superheat increases.
    Apr 2001
    79
    5,071
    35
    I'm thinking 60-70% of dT would work better than 60-70% of TD, but again this is a rule of thumb and has its limitations and exceptions.
  1. Refrigeration 101
    By Gary in forum Fundamentals
    Last Post: 01-11-2011, 10:18 PM
  2. 9 superheat & subcooling scenarios
    By nike123 in forum Fundamentals
    Last Post: 19-07-2011, 03:16 AM
  3. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Last Post: 15-01-2011, 01:24 AM
  4. Compressor loading, cooling, and range of operation.
  5. Superheat
    Last Post: 23-08-2004, 05:54 PM