    Desending the Temperature in a Freezer



    Dear Friends
    In the coming weeks we have to start up a Freezer 60mx60mx12m which will work at room= -28șC

    It is conected to a two state ammonia system.
    low SST =-35șC, media SSt=-5șC, Condensing at 35șC

    We will use the SST= -5șC to keep the dock room at +5șC.

    How do you recomend to handle the start up?
    Which commpressors should we start first?
    How many steps we should use to low the temperature in the freezer?
    What conditions will difine to go to the next step?(temperature or RH)
    I appreciate your very kind comments
    regards
    Gwapa



  2. #2
    Join Date
    Sep 2009
    Location
    Idaho
    Posts
    27
    Rep Power
    0

    Re: Desending the Temperature in a Freezer

    If you have already pressure tested the system and confirmed safety/reliability, then start off in this general order:

    1. Condensor
    2. High Stage
    3. Low stage
    4. Circulation pumps and NH3 feed solenoid to evaps.
    5. Evaporator units

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Desending the Temperature in a Freezer

    Definitly the high stage first, to stabilize system before starting low stage.
    magoo

  4. #4
    Join Date
    Sep 2009
    Location
    Idaho
    Posts
    27
    Rep Power
    0

    Re: Desending the Temperature in a Freezer

    As always, be ready for the unexpected. Oftentimes pressure changes can cause flanges to leak slightly... Tighten them carefully as to not damage the gasket.

  5. #5
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: Desending the Temperature in a Freezer

    I would ramp down at 5C per day on HT system, until you get to 3C, then 1C per day until -3C hold for 5 days, then ramp down again 1-3C per day

  6. #6
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: Desending the Temperature in a Freezer

    Hi, Gwapa ,

    First run the high stage and cool down dock room at +5C

    ... when you have all under control - high stage is running in auto mode - then start low stage compressors

    ... keep in mind to not go too fast down to -28C follow suggestion of mad fridgie

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  7. #7
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: Desending the Temperature in a Freezer

    Thanks for your very kind advices

    As long I start the low stage I should ajust the evaporator temperature at (let say) +10șC in orther to have a room temperature +15șC.
    Then ajust 0șC to get a room temperature at +5șC

    Then ajust at -5șc to get a RT 0șC

    At this moment I would need to defrost the evaporators
    and so on

    Am I right???
    need I to check the Relative Humidity?
    Thanks again
    gwaa

  8. #8
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Desending the Temperature in a Freezer

    Hi Gwappa.
    Hopefully you have designed with a PLC to control all systems, and not relying on manual ( human factor ) control.
    magoo

  9. #9
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: Desending the Temperature in a Freezer

    Thanks Magoo
    Yes we did design in a net.
    All signal go to a main computer and all the logic is there.

    However I am curious how will be the behavier of the low stage compressors runnig at to high succion pressure during the lowering temperature period
    regards
    gwapa

  10. #10
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Desending the Temperature in a Freezer

    If you have a dual duty compressor use it for both chiller and freezer initially on chiller duty controls .

    Bring temp down slowly and have doors cracked open so you don't accidentally implode cool room / freezer ( it has happened but don't let it happen to you ) .
    Hold rooms at 5 deg C as long as you can , say min 4-5 days and measure floor temp . If down to temp then gradually bring temp down over another 3-4 days .
    Concrete will hold a lot of heat especially if new .

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 02:24 AM
  3. LG heat pump problem
    By back2space in forum Heat Pumps
    Replies: 132
    Last Post: 02-02-2009, 12:23 AM
  4. TK basic micro-p features and functions
    By REEFER-TEK in forum Transport
    Replies: 0
    Last Post: 05-12-2007, 07:25 PM
  5. Article in ACH&R News
    By Gary in forum Fundamentals
    Replies: 8
    Last Post: 20-05-2003, 12:27 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •