Thread: Measuring Airflow
17-09-2009, 08:59 PM #1
Measuring Airflow
What is the general rule of thumb to determine enough airflow for condensors and evaporators? I've read that is around 300 cubic feet per minute per kw, is this right?
Also i have the testo 510-2 that measure airflow, temperature and humidity but it measures airflow in metres per second or feet per minute.
How do i convert cubic feet per minute to feet per minute?
Marc
17-09-2009, 10:54 PM #2
Re: Measuring Airflow
Take area of grille, coil etc.
Width x height in metres or feet-inches
Metric:-
1.5m x 0.5m = 0.75 sq.m.
Measured velocity in m/s
Lets say m/s = 2.5
Volume or air flow rate = 2.5m/s x 0.75sq.m = 1.875 cu.m/s
Imperial would be ft x ft x fpm = cfm.
When measured airflow across the coil using an anemometer divide the coil face into equal areas and take a velocity reading in the centre of each area. Then take the average of those readings.Brian - Newton Abbot, Devon, UK
17-09-2009, 11:12 PM #3
that will work with return grilles the air is not jetting out of them
for supply grilles you need to get an "Ak" factor or "Free area" to correct the jetting air stream's velocityTake the V out of HVAC and you are left with a HAC job
18-09-2009, 06:29 PM #4
I have thermo king sbIII it is 1996, whats is corectly arpm in my unit.
thanks
18-09-2009, 11:08 PM #5
Some duct measuring details here for position of anemometer/pitot static tube.
http://www.omega.co.uk/green/pdf/AIRFLOW_MEAS_REF.pdfBrian - Newton Abbot, Devon, UK
19-09-2009, 08:55 AM #6
Thanks Brian, i'll have a read through that.
Marc
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
Measuring performance
By Larry2 in forum FundamentalsReplies: 8Last Post: 12-02-2010, 03:49 PM -
AHU Calculations
By SUBCONTRACTOR in forum FundamentalsReplies: 20Last Post: 07-11-2009, 04:51 AM -
Quick Check for Sizing Units to enough Airflow
By udarrell in forum Air ConditioningReplies: 1Last Post: 04-07-2009, 10:49 PM -
airflow
By bangoman in forum Air ConditioningReplies: 13Last Post: 13-11-2008, 06:55 PM