    R410a evaporative condenser



    Hi sirs

    is there any manufacturer producing r410a evaporative condenser ? it it better performance than R22 one? hope somebody can help me about it. thanks in advance!


    regards
    LC


    I hear...I forget;I see...I remember;I do...I understand

  2. #2
    Join Date
    Dec 2009
    Location
    usa
    Posts
    6
    Rep Power
    0

    Re: R410a evaporative condenser

    I don't know of any; I think the pressures of R410A may be too high. Might check with Recold.

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: R410a evaporative condenser

    So long as it rated for operational pressures, where is the problem. Total heat of rejection is the primary factor.

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: R410a evaporative condenser

    The manufacturers should be able to give you a correction factor for R-410a. Since they already have R-22 ratings I suspect the correction factor would be based on the R-22 data.

    I looked at this one time. R-410a looks like a good refrigerant except for the high pressure. If you use a lower condensing temperature you should be below the manufacturers maximum pressure rating.
    If all else fails, ask for help.


  5. #5
    Join Date
    Dec 2009
    Location
    utah
    Age
    53
    Posts
    7
    Rep Power
    0

    Re: R410a evaporative condenser

    Dont use an r-22 coil, there rated at 300 psi. 410-a is rated to 450 psi. on residental and most light commerical package units as well. Hope this helps.

  6. #6
    Join Date
    Dec 2009
    Location
    utah
    Age
    53
    Posts
    7
    Rep Power
    0

    Re: R410a evaporative condenser

    Oh most manufactures have coils rated for both but you need the correct txv.

  7. #7
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: R410a evaporative condenser

    The condensing temperature/pressure will determine the required design pressure. If it's air-cooled then the design pressure would of course be much higher.
    If all else fails, ask for help.


Similar Threads

  1. Evaporative Condenser in reverse cycle
    By Friobernal in forum Industrial
    Replies: 6
    Last Post: 16-04-2009, 02:06 PM
  2. R410A water cooled condenser
    By K.R.Iyer in forum Fundamentals
    Replies: 0
    Last Post: 04-02-2009, 02:10 AM
  3. Evaporative Condenser Presure Lost
    By gwapa in forum NH3
    Replies: 9
    Last Post: 16-02-2008, 10:02 AM
  4. Evaporative Condenser
    By tjk2007 in forum Supermarket Refrigeration
    Replies: 1
    Last Post: 07-10-2007, 09:00 PM
  5. Evaporative condenser pipe surface
    By Gonzalo Arias in forum Tools and Calculators
    Replies: 0
    Last Post: 03-08-2005, 12:33 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •