    Sep 2009
    Australia
    73
    7
    Maximum water ppm levels for refrigerants
    Hi, a green newbie requiring assistance,
    We are responsible for piston compressors and high speed vane type compressors on the gas recovery refrigeration on a gas to plastic plant.
    Question is;
    " what is the 'allowable' water level in ppms the mineral oil lubricant in use?"
    Our test results came back as 469 ppm and we resampled a day later and the water was 68 ppm, sampling proceddure and condition exactely the same.
    The concern is water was not detected in previous analysis causing other questions of
    "Can the system conceal water and release it later?"
    "Is there any chemical reaction in the system that could create water?"
    Thanks in advance for any assitance you can give
    Rob S
    Aug 2009
    New Zealand
    2,554
    26
    Re: Maximum water ppm levels for refrigerants
    What refrigerant, what oil, have you had service problems between testing (has the system been opened)
    Sep 2009
    Australia
    73
    7
    Hi MF
    Thanks for the reply
    I'm talking with them tommorrow and will get the info,
    Thanks and regards
    Rob S
    (Me Wairarapa Boy, what area are you guys from)
    Aug 2009
    New Zealand
    2,554
    26
    Rangiora (chch)
    3,356
    Oil added to system , is it sealed or open to atmosphere where it could absorb moisture or water .
    Maybe you could sample it for a base .
    Also does system run in a vacuum as I'm assuming its on ammonia ?
    How old is system and is the water effecting anything that you know of ?
    Sep 2009
    Australia
    73
    7
    Cool Re: Maximum water ppm levels for refrigerants
    Quote Originally Posted by mad fridgie View Post
    Hi Thanks for the asstance
    The Carrier chillers operate on Hydrofluorocarbon (HFC) R 134a
    Each chiller has a nominal charge of approximately 748 Kg per chiller.
    OIL MANUFACTURER: CASTROL
    OIL TYPE: ICEMATIC SW
    We are wishing to know the maxppm water for stability and also Max TAN before servicing
    Thanks in advance for the assitance
    regards
    Rob S
  1. Fact or Fiction
    By david.findlay in forum Fundamentals
    Last Post: 09-03-2009, 06:19 PM
  2. pure water from air
    Last Post: 26-02-2009, 12:25 PM
  3. Modifying aricond. for heating, cooling and hot water
    By kimusabi in forum Technical Discussions
    Last Post: 10-10-2008, 07:28 AM
  4. open cycle R718 A/C that also provides high purity water?
    By star882 in forum Technical Speculations
    Last Post: 27-07-2006, 04:18 AM
  5. Building a wine cabinet