    Angry 24000btu split / l/s too high



    hi all,
    i repaced a compressor on a 24000btu split unit,
    the problem i have at the moment is when the unit is in cooling & i am pulling R22 into the system, the low side is on 410psi, the pipes are still frozen, so i must add more gas for the pipes to sweat, but when i turn off the unit the low side gauge reaches 1500psi.
    if i put the unit to heat mode the pipes get so hot, & the compressor kicks out, there is no air in the system & is pure R22, any ideas



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: 24000btu split / l/s too high

    1500 psi means that you have bomb!
    Check again your readings!
    Is it PSIA or PSIG?
    Did you replaced compressor with original one or with some kind of replacement of different make and model#?
    What is expansion device?
    Did you find what is killed previous compressor?
    Charge that unit using scale and weight at nameplate!!!

  3. #3
    Join Date
    Aug 2009
    Location
    Turhona.libya
    Posts
    79
    Rep Power
    15

    Re: 24000btu split / l/s too high

    It's better if you use another gauges and reread the pressure as the given readings sound unrealistic ,also get the RLA. , the LRA ,voltage , and the ph of the new and the old compressor from the name plates .

  4. #4
    Join Date
    Sep 2009
    Location
    Gauteng
    Age
    51
    Posts
    16
    Rep Power
    0

    Re: 24000btu split / l/s too high

    gauges were not too health, changed gauges, on cooling l/s =50 psi - 3.2 bar. unit off l/s = 144 psi - 10 bar.
    still to high, pipes still frozen, evap coils still freezing. going to recover the gas & start again, compressor is exactly the same as old comp, the other comp was miswired & burnt out.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: 24000btu split / l/s too high

    Quote Originally Posted by Draco View Post
    gauges were not too health, changed gauges, on cooling l/s =50 psi - 3.2 bar. unit off l/s = 144 psi - 10 bar.
    still to high, pipes still frozen, evap coils still freezing. going to recover the gas & start again, compressor is exactly the same as old comp, the other comp was miswired & burnt out.
    Is your pressures absolute or relative (psia or psig)?
    Expansion device type?
    Indoor air in and out DB and WB temperatures?
    Suction pipe temperature?
    Did you charge it by nameplate + additional charge for pipe length higher than unit is precharged for.

  6. #6
    flarenut40's Avatar
    flarenut40 Guest

    Re: 24000btu split / l/s too high

    Hi Draco
    1st thing I would do is look at the indoor unit and see if there is any reason the evap is not getting good heat exchange between the Refrigerant and the Air - ie Blocked filter, blocked coil fan speed too low.
    I would expect the gauges to read around HS 15bar, LS between 4 and 5bar depending o the ambient temp and the room temp.
    Like Nike123 said if you measure/calculate and weigh the charge into the system then you eliminate any guess work and you know something else is wrong, and problably contributed to the failure of the original compressor. Good Luck

  7. #7
    Join Date
    Apr 2009
    Location
    WI USA
    Posts
    27
    Rep Power
    0

    Re: 24000btu split / l/s too high

    It sounds like an extremely low heatload on the evaporator.

    I would not be running it that way until you locate & eliminate the cause, it could damage the new compressor. - Darrell

  8. #8
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: 24000btu split / l/s too high

    Did you weigh in the correct refrigerant charge as per manufacturers label on the outdoor unit.
    Quite often when stopped the reversing valve will unload and equalise system for low starting torque requirements.
    Double check your service gauges as being accurate.
    magoo

Similar Threads

  1. need help! compressor kicking out on high pressure
    By SloFuse in forum Trouble Shooting
    Replies: 16
    Last Post: 19-08-2009, 04:46 PM
  2. Sensible Heat Factor / capacity of Inverter split Systems at part load?
    By Greengrocer in forum Technical Speculations
    Replies: 31
    Last Post: 09-02-2009, 04:57 PM
  3. High Efficiency Mini Split for High Humidity Area
    By Joybob in forum Air Conditioning
    Replies: 27
    Last Post: 07-04-2008, 11:06 PM
  4. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  5. High overcurrent on 3.5kW heatpump split
    By Makeit go Right in forum Air Conditioning
    Replies: 12
    Last Post: 08-03-2007, 12:27 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •