    LoCK out Relay functioning



    Can anyone tell me What is lOck out Relay with
    associated circuit diagram ?
    Advanced thanks



  2. #2
    Join Date
    Aug 2009
    Location
    Turhona.libya
    Posts
    79
    Rep Power
    15

    Re: LoCK out Relay functioning

    Locked out relays are electromagnetic switch with normally open and normally closed contacts. Their functions according to how they are connected in the circuit.

  3. #3
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    545
    Rep Power
    18

    Re: LoCK out Relay functioning

    typically they will be triggered when a safety switch opens such as low pressure or high pressure condition. The system will be off until the power is reset
    Take the V out of HVAC and you are left with a HAC job

  4. #4
    Join Date
    Sep 2009
    Location
    NYC
    Age
    39
    Posts
    9
    Rep Power
    0

    Re: LoCK out Relay functioning

    Quote Originally Posted by Shibhrac View Post
    Locked out relays are electromagnetic switch with normally open and normally closed contacts. Their functions according to how they are connected in the circuit.
    Quote Originally Posted by Abby Normal View Post
    typically they will be triggered when a safety switch opens such as low pressure or high pressure condition. The system will be off until the power is
    reset
    First some statements:
    1. The lockout relay has a high impedance coil.
    2. Electricity will always go the easiest through a circuit (to ground).

    How it works:
    under normal operation the current going through the lockout relay coil will not be enough to energize the coil.
    ones one of the safeties trips, the easiest current path will be
    through the lockout relay coil and compressor contactor (CC). ones the lockout relay is energized is will open the NC switch on it, and prevent compressor from starting. even when the safety returns to NC position. in order to reset the lockout relay power must be broken to the lockout rely coil.

    [IMG]file:///tmp/moz-screenshot.jpg[/IMG]

  5. #5
    Join Date
    Sep 2009
    Location
    NYC
    Age
    39
    Posts
    9
    Rep Power
    0

    Re: LoCK out Relay functioning

    [quote=myrsve;161817]First some statements:
    1. The lockout relay has a high impedance coil.
    2. Electricity will always go the easiest through a circuit (to ground).

    How it works:
    under normal operation the current going through the lockout relay coil will not be enough to energize the coil.
    ones one of the safeties trips, the easiest current path will be
    through the lockout relay coil and compressor contactor (CC). ones the lockout relay is energized is will open the NC switch on it, and prevent compressor from starting. even when the safety returns to NC position. in order to reset the lockout relay power must be broken to the lockout rely coil.

    lockout relay.jpg

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: LoCK out Relay functioning

    Here is basic diagram with memory relay which I just draw (function as High Pressure trip memory and alarm).

    Last edited by nike123; 26-09-2009 at 06:26 PM.

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: LoCK out Relay functioning

    Quote Originally Posted by nike123 View Post
    Here is basic diagram with memory relay which I just draw (function as High Pressure trip memory and alarm).

    Hmmm... that doesn't look quite right. I think the HP pressurestat is hooked up wrong. It should tie in on the other side of the 1K3 contacts, so that it can energize the relay.
    Last edited by Gary; 27-09-2009 at 01:03 AM.

  8. #8
    Join Date
    Sep 2009
    Location
    NYC
    Age
    39
    Posts
    9
    Rep Power
    0

    Re: LoCK out Relay functioning

    Quote Originally Posted by nike123 View Post
    Here is basic diagram with memory relay which I just draw (function as High Pressure trip memory and alarm).
    corrected some mistakes you made
    3956376204_b9bfe038ef_o.png

  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: LoCK out Relay functioning

    Quote Originally Posted by myrsve View Post
    corrected some mistakes you made
    3956376204_b9bfe038ef_o.png
    Sorry but that is also wrong. It should be as Gary said.
    And it was at first, when I draw it, but I made some rearrangement for better look and made mistake with that connection.



    Now to explain this diagram. Above is display of de-energized contacts of memory relay as it appears in electrical diagrams by EN standard


    1. Normal state
      When there is no error, compressor contactor is energized/de-energized by thermostat 1B1 thru 21-22 NC contacts of 1K3 memory relay. Memory relay is de-energized since HP pressure contact is NO type and open when pressure is below set value (close on rise). Also, memory relay 13-14 NO contact is open and circuit cannot be closed thru it. Signal lamp is de energized because of NO contact 33-34 of memory relay.
    2. HP error present
      HP pressurestat NO contact is closed and memory relay is energized. Contacts of relay switch position, and NC contact 21-22 became open and cut off supply to contactor. NO contact 13-14 is now closed and memory relay is also energized thru that contact. NO contact 33-34 closes and alarm lamp is energized.
    3. HP error is not present, memory effect
      HP pressure error stops and pressurestat NO contact is open, but memory relay is energized thru its own NO contact 13-14 (now closed) and closed push button NC contact, and everything else remains same as if the high pressure error is still present.
    4. Trying to reset with high pressure error still present
      Pressurestat NO contact is closed and memory relay is still energized. Push button is pressed (NC contact opens) and circuit is interrupted between live and 13 connection, but connection 14 is energized thru now closed NO contact of HP pressurestat. Nothing changes and reset could not be done when high pressure is still present.
    5. Reset when there is no high pressure error
      HP pressurestat NO contact is open, and by briefly opening NC contact at reset button, memory relay is de-energized.
      Before switchover:



      After:

      Its contacts switch position and NO contact 13-14 is now open. When push button is depressed, memory relay is not energized because open NO contact 13-14 and HP pressurestat NO contact are now open contacts. NO contact 33-34 is also open and alarm lamp is de-energized. NC contact 21-22 is now closed and contactor could be energized/de-energized thru termostat contacts.


    Guys, correct me if I draw something wrong, i will fix it!
    Last edited by nike123; 27-09-2009 at 09:43 AM.

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: LoCK out Relay functioning

    Quote Originally Posted by Gary View Post
    Hmmm... that doesn't look quite right. I think the HP pressurestat is hooked up wrong. It should tie in on the other side of the 1K3 contacts, so that it can energize the relay.
    Yep, you are right! I made correction.

  11. #11
    Join Date
    Sep 2009
    Location
    NYC
    Age
    39
    Posts
    9
    Rep Power
    0

    Re: LoCK out Relay functioning

    Quote Originally Posted by nike123 View Post
    Sorry but that is also wrong. It should be as Gary said.
    And it was at first, when I draw it, but I made some rearrangement for better look and made mistake with that connection.
    !
    okay I see you point. but my drawing is not wrong. it will still work the only difference it the light will go off when there is a trip.
    my only concern is that in your drawing, if there is a wire break between the HP switch and connection point. the unit will not trip on Highhead.

  12. #12
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: LoCK out Relay functioning

    Quote Originally Posted by myrsve View Post
    okay I see you point. but my drawing is not wrong. it will still work the only difference it the light will go off when there is a trip.
    my only concern is that in your drawing, if there is a wire break between the HP switch and connection point. the unit will not trip on Highhead.
    Ok, but then Reset push button should be renamed as Start push button and signal lamp function is then to signal corect operation not alarm condition.




    Also, in your first drawing, there is no thermostat.
    Correct me if I am wrong, but if you place thermostat anywhere, that circuit will reset itself whenever termostat is not calling, if placed out of relay loop, and it will activate lock out if placed inside relay loop.
    Function of lock-out relay (in our examples) is to forbid function of compresor until power is interupted or error is no more present but manually reset must be done.
    In your example, if we introduce thermostat, that is not the case:

    Last edited by nike123; 29-09-2009 at 06:57 AM.

  13. #13
    Join Date
    Sep 2009
    Location
    NYC
    Age
    39
    Posts
    9
    Rep Power
    0

    Re: LoCK out Relay functioning

    Quote Originally Posted by nike123 View Post
    Ok, but then Reset push button should be renamed as Start push button and signal lamp function is then to signal corect operation not alarm condition (which n.
    .
    .
    .
    Also, in your first drawing, there is no thermostat.
    Correct me if I am wrong, but if you place thermostat anywhere, that circuit will reset itself whenever termostat is not calling, if placed out of relay loop, and it will activate lock out if placed inside relay loop.
    Function of lock-out relay (in our examples) is to forbid function of compresor until power is interupted or error is no more present but manually reset must be done.
    In your example, if we introduce thermostat, that is not the case:
    First: there is a thermostat. Y1 is a stander marking for 1. stage cooling on thermostats. at least here in the US, in the relation to air conditioning.

    second: yes it is true that if the thermostat cycles of it will reset the lockout relay. that means that the thermostat needs to meet setpoint to cycle of or some one will need to manually cycle the thermostat.

    third: in your circuit if there is a power interruption between L and N. Your system will reset on it own.
    PS: nice drawings. I miss the IEC drawings, don't see them over here. except on PETRA units.

    Four: the person asked for a lockout relay. I drew what came to mind. Checkout icm controls if you have time

  14. #14
    Join Date
    Sep 2009
    Location
    NYC
    Age
    39
    Posts
    9
    Rep Power
    0

    Re: LoCK out Relay functioning

    scan0065.jpg
    here is a update. hope fully everybody understands this one.
    PS: How do I edit my post. so i don't have to repost for every little thing.

  15. #15
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: LoCK out Relay functioning

    Quote Originally Posted by myrsve View Post
    scan0065.jpg
    here is a update. hope fully everybody understands this one.
    PS: How do I edit my post. so i don't have to repost for every little thing.
    At the bottom of each of your post should be EDIT button.

  16. #16
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: LoCK out Relay functioning

    Quote Originally Posted by myrsve View Post

    Four: the person asked for a lockout relay. I drew what came to mind. Checkout icm controls if you have time
    Me too. Sorry if you see this as competition. It was not that!
    It is only different approach! And it is good thing because interested could learn about pro and contra of each approach.

    What is Icm controls? Company you work for?
    Last edited by nike123; 29-09-2009 at 06:45 AM.

  17. #17
    Join Date
    Sep 2009
    Location
    NYC
    Age
    39
    Posts
    9
    Rep Power
    0

    Re: LoCK out Relay functioning

    Quote Originally Posted by nike123 View Post
    Me too. Sorry if you see this as competition. It was not that!
    It is only different approach! And it is good thing because interested could learn about pro and contra of each approach.

    What is Icm controls? Company you work for?
    It was fun ville it lasted. it is a good thing to see problems from different perspectives.

    ICM controls is a controls products company. i don't have the minimum post count to link the web address.
    icmcontrols . com

Similar Threads

  1. Relay sparks!!!! cooler not going cold!!!
    By coolrunnings1 in forum Fundamentals
    Replies: 13
    Last Post: 07-07-2009, 04:29 AM
  2. Hermetic analyzer " ANNIE" how do they work
    By kengineering in forum Tools and Calculators
    Replies: 11
    Last Post: 02-03-2008, 07:10 PM
  3. voltage drop on relay
    By Temprite in forum Electrical
    Replies: 4
    Last Post: 30-01-2006, 08:55 PM
  4. Potential Relay not staying open
    By labrosse in forum Technical Speculations
    Replies: 4
    Last Post: 05-08-2005, 08:14 PM
  5. Freezer Potential Relay not staying open
    By labrosse in forum Trouble Shooting
    Replies: 0
    Last Post: 28-10-2003, 02:53 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •