    Design Return Gas Temperature (RGT):



    Dear Friends
    The following statement was taken from Carlyle compressor selection software.
    Design Return Gas Temperature (RGT):
    A data field for entering the design RGT for the refrigeration system. This temperature is generally selected as 25 ºFdegrees for Low Temperature applications and 40 ºFdegrees for Medium Temperature applications but may be any temperature equal to or greater than the SST (Saturated Suction Temperature) and less than or equal to 65F (65F is the default).

    It is a very wide criterio ¿ Could somebody make this criterio narrow?
    If I have -35ºC SST/ Condensing at +40ºC and using screw compressor,subcooling and economizer, which RTG should I select?
    I appreciate your very kind comments
    Best regards
    Gwapa



  2. #2
    Join Date
    Jul 2009
    Location
    Brisbane
    Age
    67
    Posts
    79
    Rep Power
    15

    Re: Design Return Gas Temperature (RGT):

    I have always used a rule of thumb of not more than 20K suction gas return. I think that equates to about 35R in imperial.Basically if the elevated RST is not producing useful cooling your cop will decrease. Also, especially at low SST on some refrigerants, High RSTs will produce high discharge temperatures that can cause valve coking and oil carbonising

  3. #3
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: Design Return Gas Temperature (RGT):

    Thanks Oldesky
    When you specify 20K=36R, it is over the SST.
    that is RGT=SST+20K

    Carlyle specify -3,9ºC for low temperature and 4,4ºC for media temperatura. But it could be any between SST and 18,3ºC

    So you will be a little higher if you figure aout with 20K

    I appreciate your very kind answer
    Regards
    Gwapa

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 02:24 AM
  3. Design Return Gas Temperature (RGT):
    By gwapa in forum Commercial
    Replies: 0
    Last Post: 13-09-2009, 01:44 PM
  4. LG heat pump problem
    By back2space in forum Heat Pumps
    Replies: 132
    Last Post: 02-02-2009, 12:23 AM
  5. Article in ACH&R News
    By Gary in forum Fundamentals
    Replies: 8
    Last Post: 20-05-2003, 12:27 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •