Pressure transducer problem
I was working on a Lennox unit KVHK48D the other day that has 2 circuits each circuit has 1 compressor, 1 accumulator , 1 condensor fan etc.
My problem is circuit 2 was tripping on HP due to high head pressure caused by an actuator that controlls dampers (which were closed) for the head pressure but each circuit doesnt have a seperate actuator/damper they share 1 on the condensor coil.
Also the pressure transducer that controlls the actuator is in the discharge line of circuit 1 only.
When circuit 2 starts up alone then the dampers are closed causing the HP to rise, it's only when circuit 1 starts up that the dampers begin to open.
For the life of me i can't figure out how it is supposed to work.
Why only have 1 pressure transducer controlling 2 circuits?
The difference between genius and stupidity is that genius has its limits.
Marc
-
13-09-2009, 11:01 PM #2
Re: Pressure transducer problem
Perhaps circuit 1 is the duty circuit and and second one kicks in when the load increases.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
14-09-2009, 06:59 AM #3
Re: Pressure transducer problem
That could be the case but the 2nd one starts up before the first one sometimes.
I tried ringing technical to ask them but i was put through to a guy in France that didn't know.The difference between genius and stupidity is that genius has its limits.
Marc
Similar Threads
-
Daikin Pressure Transducer
By Pingo in forum Air ConditioningReplies: 3Last Post: 08-09-2009, 08:56 PM -
Capillary Tube Characteristics
By Chef in forum FundamentalsReplies: 9Last Post: 10-03-2009, 02:03 PM -
Screw compressor system losing oil differential pressure
By orm in forum Trouble ShootingReplies: 27Last Post: 27-10-2006, 03:19 AM -
Interesting Problem
By NH3LVR in forum Industrial CompressorsReplies: 13Last Post: 12-08-2006, 10:27 PM -
water pressure problem
By Renato RR in forum Technical SpeculationsReplies: 3Last Post: 13-02-2006, 08:54 AM