    Pressure transducer problem



    I was working on a Lennox unit KVHK48D the other day that has 2 circuits each circuit has 1 compressor, 1 accumulator , 1 condensor fan etc.

    My problem is circuit 2 was tripping on HP due to high head pressure caused by an actuator that controlls dampers (which were closed) for the head pressure but each circuit doesnt have a seperate actuator/damper they share 1 on the condensor coil.

    Also the pressure transducer that controlls the actuator is in the discharge line of circuit 1 only.
    When circuit 2 starts up alone then the dampers are closed causing the HP to rise, it's only when circuit 1 starts up that the dampers begin to open.

    For the life of me i can't figure out how it is supposed to work.

    Why only have 1 pressure transducer controlling 2 circuits?


    The difference between genius and stupidity is that genius has its limits.

    Marc

  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Pressure transducer problem

    Perhaps circuit 1 is the duty circuit and and second one kicks in when the load increases.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,876
    Rep Power
    28

    Re: Pressure transducer problem

    That could be the case but the 2nd one starts up before the first one sometimes.

    I tried ringing technical to ask them but i was put through to a guy in France that didn't know.
    The difference between genius and stupidity is that genius has its limits.

    Marc

Similar Threads

  1. Daikin Pressure Transducer
    By Pingo in forum Air Conditioning
    Replies: 3
    Last Post: 08-09-2009, 08:56 PM
  2. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 02:03 PM
  3. Replies: 27
    Last Post: 27-10-2006, 03:19 AM
  4. Interesting Problem
    By NH3LVR in forum Industrial Compressors
    Replies: 13
    Last Post: 12-08-2006, 10:27 PM
  5. water pressure problem
    By Renato RR in forum Technical Speculations
    Replies: 3
    Last Post: 13-02-2006, 08:54 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •