Results 1 to 12 of 12

Thread: Trane ERTHA300

  1. #1
    Join Date
    Nov 2004
    Location
    uk
    Age
    77
    Posts
    61
    Rep Power
    20

    Question Trane ERTHA300



    About six months ago I replaced an unloader piston seal on one of three units on a site...complete stripdown was required and Trane were involved with the project from the word go.
    On the same machine I now have an oil diff tripping problem..I first changed the filter but the problem persists...I notice that after about a minute of running (the oil switch is timed on startup) that the separator sump gets very cold as do the oil pipes...I have contacted Trane and the only common cause of carrying liquid over on these machines would normally be either overcharged (The charge was weighed into this machine) or low evaporator water flow...(the flow is fine and matches the other two units on site which run well).
    I am wondering if the unloader piston seal has had a catastrophic failure allowing the full bore pipe of oil to bypass the seal and go straight into the suction side(where it would bleed slowly to when unloading normally)...would this chill down the whole oil sump in a short time????....on the last try I gave it I turned the controller switch to load and left it there.....there was NO increase in machine amps at all over the total run time of say two minutes....has anyone else had a problem similar to this????


    Not getting wiser at the same rate as I am getting older??

  2. #2
    PETER MAHONEY's Avatar
    PETER MAHONEY Guest

    Re: Trane ERTHA300

    Hi
    Check the oil pressure drop across the filter & check that the oil pressure switch is closing on start up

  3. #3
    Join Date
    Dec 2008
    Location
    UK
    Posts
    55
    Rep Power
    16

    Re: Trane ERTHA300

    John, Is that You??

  4. #4
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: Trane ERTHA300

    hello superheatman what compressor model do you have on this chiller

  5. #5
    Join Date
    Nov 2004
    Location
    uk
    Age
    77
    Posts
    61
    Rep Power
    20

    Re: Trane ERTHA300

    Quote Originally Posted by GHAZ View Post
    hello superheatman what compressor model do you have on this chiller
    Hi...sorry..left details in vehicle...will reply when back at work.
    Not getting wiser at the same rate as I am getting older??

  6. #6
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Trane ERTHA300

    What are chilled and cooling water temperatures during start up?
    If it ain't broke, don't fix it!

  7. #7
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    54
    Posts
    282
    Rep Power
    15

    Re: Trane ERTHA300

    DEAR FRIEND
    CHECK THE CONNECTIONS OF THE DIFFERENTIAL PRESSURE SWITCH OIL, OTHER CAUSE THAT IS THAT MAY BE WATER COOLING TOWER is very cold, typically when the valve seal is damaged COMPRESSOR NO CHARGE IF YOU NEED TO HAVE THE MANUAL OF FAILURE OF RTHA300

  8. #8
    Join Date
    Aug 2001
    Location
    Gold Coast, Australia
    Posts
    600
    Rep Power
    28

    Re: Trane ERTHA300

    Quote Originally Posted by PETER MAHONEY View Post
    Hi
    Check the oil pressure drop across the filter & check that the oil pressure switch is closing on start up
    Pete, I have this feeling in the back of my head that Basingstoke had this problem with an early RTHA. Might be worth checking with AA or TW? It's too long since I last worked there to remember for sure.

  9. #9
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Trane ERTHA300

    Quote Originally Posted by Superheatman View Post
    About six months ago I replaced an unloader piston seal on one of three units on a site...complete stripdown was required and Trane were involved with the project from the word go.
    On the same machine I now have an oil diff tripping problem..I first changed the filter but the problem persists...I notice that after about a minute of running (the oil switch is timed on startup) that the separator sump gets very cold as do the oil pipes...I have contacted Trane and the only common cause of carrying liquid over on these machines would normally be either overcharged (The charge was weighed into this machine) or low evaporator water flow...(the flow is fine and matches the other two units on site which run well).
    I am wondering if the unloader piston seal has had a catastrophic failure allowing the full bore pipe of oil to bypass the seal and go straight into the suction side(where it would bleed slowly to when unloading normally)...would this chill down the whole oil sump in a short time????....on the last try I gave it I turned the controller switch to load and left it there.....there was NO increase in machine amps at all over the total run time of say two minutes....has anyone else had a problem similar to this????
    hi does your head pressure control work?
    off hand it seems like u have a leek in oil pressure that would cause this trip .
    if this problem did not occur before u are right to zero in on the seal ofc the unloader system .
    if u are not able to load the comp manualy u deffinatly have a proble with oil pressure reaching the slide valve or the seal on the valve is broken ,u also might have an obstruction in the oil pass not letting oil into the loader u should check this attached article should shed some light on your problem
    http://trane.com/Commercial/Uploads/...N_09012005.pdf
    mail me at gill@gosheneng.co.il i will mail u the slide valve manual from trane!

  10. #10
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    54
    Posts
    282
    Rep Power
    15

    Re: Trane ERTHA300

    VALVE TAKE CHARGE AND DISCHARGE OF A FILTER BRONZE sometimes obstruct, CHECK TO OPEN THE CONTACTS OF THE DIFFERENTIAL PRESSURE SWITCH OIL, OIL PRESSURE MEASURED OUTPUT FILTER WING AND UPPER WINGS NEAR COMPRESSOR LOAD SOLENOID , CHECK THAT IS NOT SOME CAPILLARY DUCT

  11. #11
    Join Date
    Aug 2008
    Location
    London
    Age
    42
    Posts
    55
    Rep Power
    16

    Re: Trane ERTHA300

    Can anyone advise the procedure for changing the oil filter on a RTHA?

    Thanks in advance

  12. #12
    Join Date
    Oct 2010
    Location
    Greece
    Age
    52
    Posts
    97
    Rep Power
    14

    Re: Trane ERTHA300

    Hi wilko,
    Please check attachment.
    Please always create a new post!
    Regards,
    CV
    Attached Files Attached Files

Similar Threads

  1. AEC Pinical chiller with trane comp
    By cptrdbrd in forum Commercial
    Replies: 1
    Last Post: 28-10-2009, 09:47 PM
  2. trane ertaa213 EEV fault (1AA)
    By knight rider in forum Technical Discussions
    Replies: 4
    Last Post: 11-06-2009, 06:40 AM
  3. New to Forum, Facing problems related with TRANE Chiller
    By neerajpuranik in forum Air Conditioning
    Replies: 3
    Last Post: 10-12-2008, 02:43 AM
  4. Trane CVHE 450 R11 Centrifugal Chiller
    By albertjoseph in forum Air Conditioning