Results 1 to 5 of 5
Thread: RS-44 (R424a)
  1. #1
    Join Date
    Aug 2006
    Location
    Canada
    Age
    41
    Posts
    7
    Rep Power
    0
    RS-44 (R424a)
    Hello guys! (sorry for my not so good english...)
    We are on a project of replacing a 25tons york split system for an hopital in my city, but the client do not want to change the fan/coil section and want to try the new R424A. Our first price was based on a full change to R410(Compressor section and fan coil), but the price is too high for them...
    So we will use a R22 condensing unit retrofited with R424a...
    My question is; How do R424a react in real life situation?
    PS: I know its not the best solution ever...but we got to do it with the budget of the client.
    www . rscool . com / RS-44.html
  2. #2
    Join Date
    Aug 2006
    Location
    Canada
    Age
    41
    Posts
    7
    Rep Power
    0
    Re: RS-44 (R424a)
    Sorry for the weird link.
    You are only allowed to post URLs to other sites after you have made 15 posts or more.
  3. #3
    Join Date
    Jan 2010
    Location
    UK
    Posts
    19
    Rep Power
    0
    Re: RS-44 (R424a)
    Contact national refrigerants or united refrigeration, they are in the states and canada and will give you all the advice and possible solutions
  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24
    Re: RS-44 (R424a)
    It's another blend of R125 and R134a with additional HC for helping MO carry over.
    They all are the same ****, mixed up in different way.
  5. #5
    Join Date
    Aug 2006
    Location
    Canada
    Age
    41
    Posts
    7
    Rep Power
    0
    Re: RS-44 (R424a)
    Tnx guy! The whole system has been changed with R410 unit.