    Exclamation Trane RTAD Compressor ceased



    Hi I am new to the site,

    We have a TRANE RTAD 165 unit, recently came out of warrenty, then the troubles started, new temp sensors on circuit 1, this stopped the lp cutots and superheat problems we were having running fine now. not so with circut 2. We encountered the same problems with circut 2. temp probes ordered, system pump down was attempted, lp switch fault encounted, system was then pumped down, lp switch ordered, circuit left in pumped down state. while waiting on parts , circut two tried to run, tripping the breakers on over current fault, compressor windings and contactors checked, tested ok, dignostics deemed to be a locked rotor, oil sample to be taken, what was found, no oil in the system, no leaking oil found from system. the real question I have is where would, could have the oil gone in the system to cause the locked rotor situation....



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Trane RTAD Compressor ceased

    No oil in system, that is very odd!
    Do you mean low oil level?
    How did you checked that?
    Last edited by nike123; 10-09-2009 at 09:31 AM.

  3. #3
    Join Date
    Dec 2008
    Location
    UK
    Posts
    55
    Rep Power
    16

    Re: Trane RTAD Compressor ceased

    Hi, You say the compressor ran in a pump down state- did it run into a vacuum?
    It is not advisable to run these compressors below 10psi.
    If so this could lead to a mechanical failiure.
    Also, where did you try to drain oil from?.
    At a stopped position the only reliable drain point is at the bottom of the oil separator.
    Typically -the fuses should be removed from the circuit and the circuit locked out to prevent accidental start up.
    In one instance the compressor was deliberately started reverse direction to try to free the rotors.It worked!! However this will never be endorsed by the manufacturer and could also lead to winding failiure and the additional complications of a burnout cleanup. So proceed with extreme caution. At the very least ,prime the oil circuit prior to start up. ALSO the applied voltage mustbe only for a split second. Good luck.

  4. #4
    wakefield's Avatar
    wakefield Guest

    Re: Trane RTAD Compressor ceased

    Quote Originally Posted by nike123 View Post
    No oil in system, that is very odd!
    Do you mean low oil level?
    How did you checked that?
    Hi, Samples were attempted to be taken, we could not get any oil from the bottom of the seperator, nor the oil return line, some how 11 L of oil has disappared, we now believe a faulty oil seperator or a crack in the PHE may be responsable

  5. #5
    Join Date
    Oct 2007
    Location
    Britain
    Posts
    220
    Rep Power
    17

    Re: Trane RTAD Compressor ceased

    Is the chiller oversized, continuos operation of it at part load may have resulted in most of the oil charge ending up in the evaporator.

    Cheers
    Tutto il Mondo e un Paese

  6. #6
    wakefield's Avatar
    wakefield Guest

    Re: Trane RTAD Compressor ceased

    Quote Originally Posted by El Padre View Post
    Is the chiller oversized, continuos operation of it at part load may have resulted in most of the oil charge ending up in the evaporator.

    Cheers
    Hi, thanks for the answer..

    We have had the chiller unit in for two seasons, unit set up for alternitive starts, normal load on chiller is about 66% per circuit. loads are reasonably normal. but how long at a guess would it take to take the oil charge through to the evaporator.

  7. #7
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Trane RTAD Compressor ceased

    did u find a leak?11 liters is a lot of oil !!
    did u check the evaporator?
    that is where the oil migrates to sometimes

  8. #8
    wakefield's Avatar
    wakefield Guest

    Re: Trane RTAD Compressor ceased

    Thank you to all who posted, next we are going to finish reclaiming the refrigerant, vac out and fill with dry nitrous to pressure test overnight for leaks, then investigate the evaporator etc..

  9. #9
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: Trane RTAD Compressor ceased

    verifies the distance sensors longer than if you are very inside marked mistakenly saturated evaporator temperature

  10. #10
    Dacky's Avatar
    Dacky Guest

    Re: Trane RTAD Compressor ceased

    Hi,

    One brief question, maybe you could help. I have a company that sells Goodway cleaning equipments, and to one of new customers, the service engineer quit, and the manager doesn't know the I.D. of the heat exchangers tubes in an RTAD 145, to order brushes. By any chance, don't you know?

    Thank you.

Similar Threads

  1. AEC Pinical chiller with trane comp
    By cptrdbrd in forum Commercial
    Replies: 1
    Last Post: 28-10-2009, 09:47 PM
  2. trane rtad 125 chiller, reverse phase issue
    By croc1774 in forum Air Conditioning
    Replies: 5
    Last Post: 25-08-2009, 05:44 PM
  3. trane ertaa213 EEV fault (1AA)
    By knight rider in forum Technical Discussions
    Replies: 4
    Last Post: 11-06-2009, 06:40 AM
  4. New to Forum, Facing problems related with TRANE Chiller
    By neerajpuranik in forum Air Conditioning
    Replies: 3
    Last Post: 10-12-2008, 02:43 AM
  5. Trane Defrost Control Board Energize "W" in cooling
    By jcmorris2 in forum Heat Pumps
    Replies: 6
    Last Post: 02-06-2007, 03:40 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •