    Evaporator to air TD



    Hi all

    Could anyone advise me on what a low evapotaor to air TD would indicate please ?

    I have a system which in normal running has an average 10 degc TD between evaportaor sat temp and air return , but on this paticular system i am getting only 5 degc TD,
    I am wondering if a compressor not running at full capacity due to broken valves etc would cause this ?

    any help much appreciated

    thankyou



  2. #2
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Evaporator to air TD

    If there is a lack of airflow across the evaporator then your Delta T will be large.

    A fouled evaporator causes an abnormally small Delta T for the air.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  3. #3
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Evaporator to air TD

    Sorry i read your post wrong there.

    Could you provide the figures you used to work out the low TD if you have them?
    Including superheat and subcoolinng
    The difference between genius and stupidity is that genius has its limits.

    Marc

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Evaporator to air TD

    Are you sure in your measurements?
    Last edited by nike123; 10-09-2009 at 02:27 PM.

  5. #5
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Evaporator to air TD

    An evp td has a bearing on the humidity in the cold room & it varies with product . High td means low rh & viceversa

  6. #6
    Join Date
    Jul 2002
    Location
    Derby
    Posts
    74
    Rep Power
    22

    Re: Evaporator to air TD

    Thanks guys

    I am basically asking if anything can change the TD of the Evap , ie inop fan , blockage , compressor not pumping to efficency etc.
    or is this fixed ?


    Thanks

  7. #7
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: Evaporator to air TD

    Quote Originally Posted by kfjoe View Post
    Hi all

    Could anyone advise me on what a low evapotaor to air TD would indicate please ?

    I have a system which in normal running has an average 10 degc TD between evaportaor sat temp and air return , but on this paticular system i am getting only 5 degc TD,
    I am wondering if a compressor not running at full capacity due to broken valves etc would cause this ?

    any help much appreciated

    thankyou
    A 5 degree TD is normally too low. A high humidity box such as a flower cooler runs around a 8 TD.

    Did this system work ok in the past?

    You need to note all the pertinent information such as pressures, temperatures and amperage to determine the cause.

    I would suspect loss of capacity due to a compressor problem, TEV problem, a restriction, low on refrigerant or maybe a dirty evap or fan motor problems.

    Get all the data and work from it.

    Here's a link to some troubleshooting guidelines that might help you.

    http://www.hvacrinfo.com/system_trouble.htm
    Thousands of HVACR manufacturers links! Visit: www.hvacrinfo.com

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Evaporator to air TD

    Quote Originally Posted by kfjoe View Post
    Thanks guys

    I am basically asking if anything can change the TD of the Evap , ie inop fan , blockage , compressor not pumping to efficency etc.
    or is this fixed ?


    Thanks
    I would say that is determined by evaporator construction and materials. Since both are unchanged and air flow is probably same or lower as first day, TD could only be higher.
    Are you 100% sure that your measurements and calculations is right.
    Calibrate your instruments or use calibrated.