    pressure charge



    Brod,

    i have some questions, i presently work here in riyadh ksa. our outside temp is 46-49deg celsius. my question is what is the max low press and high press charge of aircon, we are using york brand, 5tr. r-22



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: pressure charge

    the gas charge is by weight not by pressure

  3. #3
    Join Date
    Mar 2009
    Location
    South Africa
    Posts
    43
    Rep Power
    0

    Re: pressure charge

    As per sedgy. You can't alter the charge to get the unit to operate outside it's design ambient conditions.

    Best you can do it try to keep the condenser cool. Simple things like a small roof over the condenser to give it some shade is a simple start to see if the unit operates better.

  4. #4
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: pressure charge

    I think differant through experience and here it is - rule of thumb for R22 condensing pressure should be 19K to 22K above ambiant temp equivalent pressure (aircooled). And when I worked on units when the amiant went above 44C I could remove 5 - 10% weight of gas to achieve an improved cooling effect, but this gas had to go back in when the temp droped down again.

  5. #5
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: pressure charge

    Hi RC, i used to work in Dhahran, !st question is the unit sitting on concrete or directly on a roof is so you will have to raise it up. The 2nd thing you will need some sort of sunshade not to close to the condensor air discharge,if you trim the charge you will end up with the compressor over heating, it needs the refrigerant to cool the windings.

    Norm
    My wife used to say you never listen to a word I say at least I think that what she said

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: pressure charge

    Quote Originally Posted by rc_pancha View Post
    Brod,

    i have some questions, i presently work here in riyadh ksa. our outside temp is 46-49deg celsius. my question is what is the max low press and high press charge of aircon, we are using york brand, 5tr. r-22
    Are we talking about a TEV or fixed orifice system?

    What are the temperatures of the air entering and leaving the evaporator?

    What are the temperatures of the air entering and leaving the condenser?
    Last edited by Gary; 08-09-2009 at 09:54 PM.

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: pressure charge

    Quote Originally Posted by Tesla View Post
    I think differant through experience and here it is - rule of thumb for R22 condensing pressure should be 19K to 22K above ambiant temp equivalent pressure (aircooled). And when I worked on units when the amiant went above 44C I could remove 5 - 10% weight of gas to achieve an improved cooling effect, but this gas had to go back in when the temp droped down again.
    I can see where this would reduce the high side pressure, but how would it improve the cooling effect?

  8. #8
    rc_pancha's Avatar
    rc_pancha Guest

    Re: pressure charge

    ah ok. in maintenance, how can you check the unit if it is ok using gauge manifold

  9. #9
    rc_pancha's Avatar
    rc_pancha Guest

    Re: pressure charge

    ah ok.tnx. in maintenance, how can you check the unit if it is ok using gauge manifold

  10. #10
    rc_pancha's Avatar
    rc_pancha Guest

    Re: pressure charge

    Quote Originally Posted by RefrigNoob View Post
    As per sedgy. You can't alter the charge to get the unit to operate outside it's design ambient conditions.

    Best you can do it try to keep the condenser cool. Simple things like a small roof over the condenser to give it some shade is a simple start to see if the unit operates better.

    ah.ok. tnx. how can you check a unit if it is ok using gauge manifold

  11. #11
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: pressure charge

    You got your gauges on "yes"
    Discharge should be Tc (pressure temp ratio on gauge) This should be about 10C (15f) above the air entering the cond Evap te should be some what colder than the air entering the evap can not give a number, the pipe leaveing the evap should be cool and warming slightly as it reaches the comp. You NEED to check the comp motor current, it should be less than the FLA rating, but I would suggest in your conditions it would be close.
    If Tc is low and moter current is low and the suction is warm going into the comp then you need more refrigerant.
    Another good test is :
    ?
    ?
    ?
    ?
    ?
    It is doing the job, if it is leave it alone.

  12. #12
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: pressure charge

    Quote Originally Posted by mad fridgie View Post
    This should be about 10C (15f)
    1°F= 5/9°C (temperature interval)
    1°C=9/5°F (temperature interval)

    How you got this 10°C=15°F?
    It should be 10°C=10x9/5=18°F

  13. #13
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: pressure charge

    Quote Originally Posted by nike123 View Post
    1°F= 5/9°C (temperature interval)
    1°C=9/5°F (temperature interval)

    How you got this 10°C=15°F?
    It should be 10°C=10x9/5=18°F
    Just nice round numbers off the top of my head,

  14. #14
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: pressure charge

    Hi Gary
    This is only used when ambiant temps are excessive, it improves the cooling by preventing the unit from tripping out on HP safety and draws less current. This is used durring a heatwave when we get real busy and have to go around putting on band aids till we have time to fix properly. Your right it does't technicly improve the cooling it just keeps it going.

  15. #15
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: pressure charge

    Quote Originally Posted by Tesla View Post
    Hi Gary
    This is only used when ambiant temps are excessive, it improves the cooling by preventing the unit from tripping out on HP safety and draws less current. This is used durring a heatwave when we get real busy and have to go around putting on band aids till we have time to fix properly. Your right it does't technicly improve the cooling it just keeps it going.
    Quote Originally Posted by Tesla View Post
    I think differant through experience and here it is - rule of thumb for R22 condensing pressure should be 19K to 22K above ambiant temp equivalent pressure (aircooled). And when I worked on units when the amiant went above 44C I could remove 5 - 10% weight of gas to achieve an improved cooling effect, but this gas had to go back in when the temp droped down again.
    I would think that 19K above ambient (19K TD) would be the maximum, and higher efficiency systems would be lower than this.

    If this TD is exceeded, I would suspect that the system is overcharged or the evap is oversized for the condensing unit or the evap fan speed is too high.

    The fact that the refrigerant would need to be added back in after the hot weather is past seems to indicate that the load is too high (oversized evap and/or excessive evap fan speed).

    Assuming all else is working properly, near the end of the cycle the air temp exiting the evap coil should be 11K lower than the air at the thermostat. If it is less than 11K below the stat temp, then there is too much airflow. Reducing this airflow reduces the heat absorbed in the evaporator and therefore reduces the heat the condenser needs to reject, which means lower high side pressure.
    Last edited by Gary; 09-09-2009 at 07:55 PM.

  16. #16
    Join Date
    Jan 2007
    Location
    SPAIN
    Posts
    172
    Rep Power
    18

    Re: pressure charge

    Reducing the charge of gas is not the best way especially if your day/night temperature swings (as in desert conditions) are great. First wash/blow out the condenser... efficiency at rejecting heat from the system becomes critical in the described conditions when even R22 units start giving up (non condensing or hissing) and dust build up will cause this. Also what is the state of the finning: good, pitted or flakeing to pieces ? Marine exposed areas with dust lead to degradation of heat transfer because the condensers mnay be rotted.

  17. #17
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: pressure charge

    Quote Originally Posted by momo View Post
    Reducing the charge of gas is not the best way especially if your day/night temperature swings (as in desert conditions) are great. First wash/blow out the condenser... efficiency at rejecting heat from the system becomes critical in the described conditions when even R22 units start giving up (non condensing or hissing) and dust build up will cause this. Also what is the state of the finning: good, pitted or flakeing to pieces ? Marine exposed areas with dust lead to degradation of heat transfer because the condensers mnay be rotted.
    I agree with all of the above. Good advice.

Similar Threads

  1. Liquid pressure amplification (LPA)
    By US Iceman in forum New Technologies
    Replies: 34
    Last Post: 10-02-2011, 10:01 PM
  2. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 01:03 PM
  3. High Deferential Oil Pressure Alarm
    By NNNNNN in forum Trouble Shooting
    Replies: 27
    Last Post: 24-12-2007, 01:06 PM
  4. screw compressor
    By vinod in forum Trouble Shooting
    Replies: 9
    Last Post: 17-12-2005, 01:46 AM
  5. Replies: 6
    Last Post: 18-11-2005, 04:30 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •