    The noise coming from our Trane RTHD is in excess of 90 dbA and from both environmental and H&S angles, causing headaches.. It's approx 2 years old and has always been this loud.

    The noise specs at the time were, from memory, significantly less than this otherwise it would have been raised as a concern - bog standard pads are in place below the chiller but unsure if pipework is kitted out with rubber couplings as recommended in the installation manual.

    Anyone with a similar experience and if so any attenuation tips/tricks. I'm not an engineer so please go easy with the technical jargon.



  2. #2
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    18

    Re: Trane Noise

    hi have a tech check oil level and unit loading status
    these units get very noisy when oil is low and running part load

  3. #3
    Join Date
    Dec 2008
    Location
    UK
    Posts
    55
    Rep Power
    16

    Re: Trane Noise

    Hi,
    As Goshen Suggests Try and run each circuit at full load for at least 30 minutes. Stop the circuit and wait 10 minutes, and the check the oil level as per IOM. The noise could be caused by the unit running for periods of extended unloading in which the start/stop differentials should be checked and adjusted. Also check that the condenser coils are clean and that all the fans are operating as required. Good Luck.

  4. #4
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,094
    Rep Power
    23

    Re: Trane Noise

    Yes these trane screws are far too noisy. I have worked for too many hours in plantrooms with them running and are sure some frequencies in my hearing have been lost. They are especially noisy whilst unloading before shutdown.
    Noise minimisation use 2" insulation on chiller motor and compressor, ensure adiquate insulation from ground and another noise reduction method used in manufacturing is to build something like a large coolroom around each chiller. Even with earmuffs and plugs I still get headaches after a few hours of listening to them - they are in my opinion the worst chiller for noise issues, more so on the frequency range than level.

  5. #5
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    18

    Re: Trane Noise

    hi tesla :
    i agree about the noise but only part load, at full load they purr like a cat !
    i found a direct corrilation between noise and oil level
    it affects the unit especially at part load!!

  6. #6
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    621
    Rep Power
    21

    Re: Trane Noise

    Oil level and part load are indeed making them more noisy. But even cooling water temperature is a big influence on the noise level. If the cooling water temperature is high and the load is low than it will make more noise than it would at the same load with the right cooling water temperature.

    Keep in mind not to make the cooling water too low since they need a certain differential across the machine in order to keep the oil flowing!
    If it ain't broke, don't fix it!

Similar Threads

  1. AEC Pinical chiller with trane comp
    By cptrdbrd in forum Commercial
    Replies: 1
    Last Post: 28-10-2009, 10:47 PM
  2. New to Forum, Facing problems related with TRANE Chiller
    By neerajpuranik in forum Air Conditioning
    Replies: 3
    Last Post: 10-12-2008, 03:43 AM
  3. Trane CVHE 450 R11 Centrifugal Chiller
    By albertjoseph in forum Air Conditioning
    Replies: 4
    Last Post: 06-10-2008, 03:23 PM
  4. Noise induced hearing loss damages
    By Abe in forum Legal-Business-Marketing
    Replies: 7
    Last Post: 26-05-2008, 10:36 AM
  5. noise inverter compressor
    By Airclima in forum Air Conditioning
    Replies: 1
    Last Post: 26-07-2007, 11:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •