03-09-2009, 09:02 PM #1
Daikin Pressure Transducer
Hi
Maybe some one can give me some information
on a job i have to do next week where i have to replace the discharge pressure transducer on a Daikin VRV 11 system.
can anyone tell me if i need to remove all the refrigerant to do this, or can i just unscrew the transducer from the discharge line ?
One guy at Daikin tells me that i need to remove the gas another one tells me the valve is fitted with scraider fittings so i just need to unscrew it.
thanks pingo
-
08-09-2009, 08:03 PM #2
Re: Daikin Pressure Transducer
It looks like no one has done one of these!
I guess i will have to recover the gas from the unit and then fit the part
regards
pingo
-
08-09-2009, 08:37 PM #3
Re: Daikin Pressure Transducer
Hi,
Generally Hp Pressure transducers have a schraeder depressor built into them. On many systems the only time one needs to remove the refrigerant is to change a PRV or Hp switch. I would suggest that if there is a seperate Hp protection device you may be able to remove the Transducer without removing the refrigerant. Good Luck
-
08-09-2009, 08:56 PM #4
Re: Daikin Pressure Transducer
Hi Pingo,
They used to be on mushroom connectors but I think that all R410A models are not, you will have to remove the refrigerant charge.
CheersTutto il Mondo e un Paese
Similar Threads
-
High Deferential Oil Pressure Alarm
By NNNNNN in forum Trouble ShootingReplies: 27Last Post: 24-12-2007, 01:06 PM -
CPC Pressure Transducer
By thcri in forum CommercialReplies: 1Last Post: 03-02-2007, 07:43 PM -
screw compressor
By vinod in forum Trouble ShootingReplies: 9Last Post: 17-12-2005, 01:46 AM -
High pressure reading before and after condenser coil
By Cofreth in forum RefrigerantsReplies: 6Last Post: 18-11-2005, 04:30 PM