    Daikin



    having problem with a daikin inverter outside unit..keeps cutting out with the code F3 which is high temperature discharge pipe control..engineers have tested circuits re gassed gone awayand again problem comes back engineers are at a loss to explain situation..any ideas or has any one had similar problem..getting desperate temperature in mid 30s

    Martin



  2. #2
    Join Date
    Jul 2009
    Location
    Berkshire
    Age
    50
    Posts
    175
    Rep Power
    15

    Re: Daikin

    Hello Martin, we assume your engineers checked the resistance on the discharge thermistor? Even if it may be correct at ambient temperatures, it may still go awry at high temperatures.
    If at first you DO succeed, try to hide your astonishment!!

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin

    If the gas charge has been checked and adjusted to recommended levels and the thermistor is within tolerances, then I would suggest that your condenser is dirty..........

    Do you have any pressure readings?

  4. #4
    Join Date
    Dec 2007
    Location
    Birmingham
    Age
    69
    Posts
    38
    Rep Power
    0

    Re: Daikin

    Is the discharge sensor located in the pocket on the discharge line?

    I have had a few call outs when the thermistor is away from the pipe and it does not sense the heat from the discharge pipe on running,

    it can then trip out on the F3 fault.

    regards pingo

  5. #5
    Join Date
    Oct 2007
    Location
    uk
    Posts
    31
    Rep Power
    0

    Re: Daikin

    We are having the same trouble at the moment with F3 on a 407c system. We have changed thermistor, changed PCB board at daikin's recommendation, re-covered leak tested and re-gassed and is still kicking out after a while on F3. System ran for around 3 weeks after the new board was fitted and then F3. Couldn’t say if the PCB fixed anything as the fault happened sporadically anyway.
    Running pressures were fine I’m told.>>

    have splinters in my fingers now.

  6. #6
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Daikin

    Are you sure the coils are clean, they may look clean but they may not be.

    What are the condensor air on and air off temps?

    We had this problem going on for over 3 months, the guys checked everything from the fans, gas charge, sensors and cleaned the coils with a brush and RTU coil cleaner but none of it worked.

    Eventually they hired a pressure washer and cleaned the coils, that was 2 years ago and the units have never faulted on HP faults since.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  7. #7
    Join Date
    Aug 2007
    Location
    england
    Age
    40
    Posts
    4
    Rep Power
    0

    Re: Daikin

    Definately a pressure wash on the coils, I was hailed a hero when I tested out my new Karcher at work and solved the ongoing problem.

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Daikin, Why do we bother?
    By gwilliamson in forum Air Conditioning
    Replies: 21
    Last Post: 02-02-2010, 09:38 AM
  3. Daikin AC parts from UK
    By skel00 in forum Air Conditioning
    Replies: 5
    Last Post: 05-04-2009, 01:24 PM
  4. Fixing Daikin A3 Error
    By Stuffy in forum Air Conditioning
    Replies: 3
    Last Post: 27-03-2009, 06:02 AM
  5. Getting a price from Daikin....
    By monkey spanners in forum Chit Chat & Service Stories
    Replies: 4
    Last Post: 17-08-2008, 09:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •