Results 1 to 7 of 7
-
02-09-2009, 03:09 AM #1
copeland compressor btu @ 20degree evap.
I can't load my copeland program for compressor info. Can someone pull the data for me on the btu's @ a 20 or 25 degree evaporator on these compressors? Thanks
kaj-0075-tac
katb-0150-cav
rs70c1-pfv-959
-
02-09-2009, 06:15 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,175
- Blog Entries
- 6
- Rep Power
- 36
Re: copeland compressor btu @ 20degree evap.
You also need condensation temperatures. What refrigerant? What voltage, frequency, phase no.?
Check your 1st model #!Last edited by nike123; 02-09-2009 at 06:29 AM.
-
02-09-2009, 12:57 PM #3
Re: copeland compressor btu @ 20degree evap.
Please mention the refrigerant and evaporating / condensing temperature in F or C and frequency (50 Hz or 60 Hz).
-
02-09-2009, 06:39 PM #4
Re: copeland compressor btu @ 20degree evap.
CONDENSING TEMPERATURE IS 120 DEGREES AND THE TWO SEMI'S ARE R12 AND THE rs70c1-pfv-959 IS R-22 POT
-
02-09-2009, 06:41 PM #5
Re: copeland compressor btu @ 20degree evap.
They are all 1ph. And the kaj-0075 tac is correct.
-
03-09-2009, 09:38 AM #6
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,175
- Blog Entries
- 6
- Rep Power
- 36
Re: copeland compressor btu @ 20degree evap.
kaj-0075-tac
TAC mean:
T=3 phase
A=Overcurent thermal protection in the terminal block
C=3 phase 60Hz 208-230V YY/Y Part Winding
"KAJ" vith TAC in model number 3 phase 208-230 60 hz could be only KAJ1 or KAJ8
Both are low temperature application models.
20°F is medium temperature application.
Check again your model number and give us right information.
For the rest:
(btu 20°F, btu25°F) condensation 120°F
katb-0150-cav (12800, 14300)
rs70c1-pfv-959 (6930, 8090)Last edited by nike123; 03-09-2009 at 10:03 AM.
-
03-09-2009, 09:45 AM #7
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,175
- Blog Entries
- 6
- Rep Power
- 36
Re: copeland compressor btu @ 20degree evap.
...............................Double post!
Similar Threads
-
Undercharge or Dirty Evap?
By Yoz in forum Trouble ShootingReplies: 9Last Post: 19-06-2008, 01:57 PM -
iced up evap coil
By wilks in forum FundamentalsReplies: 6Last Post: 31-08-2007, 09:15 PM -
Quest sandwich cooler evap?
By The MG Pony in forum CommercialReplies: 6Last Post: 31-05-2007, 07:58 PM -
how to wire in pause before evap fan kicks in after defrost ?
By knighty in forum ElectricalReplies: 10Last Post: 21-01-2007, 02:08 AM -
Evap motor no come on
By Apprentice in forum Technical DiscussionsReplies: 13Last Post: 04-12-2003, 05:07 PM