York (YK FK FL P9-CZFS CENTIFUGAL CHILLER)
(YK FK FL P9-CZFS CENTIFUGAL CHILLER)
We have faced problem with the chiller for 1 month or more
The problem : The display of the chiller goes off which make the chiller goes down
We did a lot of trouble shooting
1. We changed the control board (work for some days then the problem came again)
2. We disconnect all I/O’s and run the display without I/O’s (display run for two days then went off again)
3. We replaced the power supply (we turn on the display only for two days it run ok then we run the chiller it had run for 3 days then same problem came again)
Can anybody help in solving this problem?
-
01-09-2009, 12:51 PM #2
Re: York (YK FK FL P9-CZFS CENTIFUGAL CHILLER)
is the power supply constant and not fluctuating..?? when you come back to the plant,is the power gone,and the display empty, ore is the display in fault/error modus?
Ice
-
01-09-2009, 12:57 PM #3
Re: York (YK FK FL P9-CZFS CENTIFUGAL CHILLER)
i think you have to check the power panel. maybe there is a fault whit the transfo. you get 400V(3+1) for the main power,and than there gose 220V(L+N) for the commands.if the trafo gets warm and let say= 280V to the command module........dont have to guess what happens. but it will be only strong enough to blow the module and not the other parts.so there is possible no burning smell.
Ice
Ice
-
02-09-2009, 07:06 AM #4
Re: York (YK FK FL P9-CZFS CENTIFUGAL CHILLER)
the power of the display did not go completely.
the display restart then when it reach to point (“initializing the application” it restart again and so on) and because of that we could not start the chiller.
-
03-09-2009, 07:11 PM #5
Re: York (YK FK FL P9-CZFS CENTIFUGAL CHILLER)
Did you checkt the power on the display??
to high....to low... and if you open the display, are there no burn marks???
i think the eprom is flasht....if it is not blown up.
Ice
-
03-09-2009, 07:13 PM #6
Re: York (YK FK FL P9-CZFS CENTIFUGAL CHILLER)
check the power supply 110v if is ok
check the inveter for display may the volt come correct from the microboard but the inveter fauiler
-
03-09-2009, 08:57 PM #7
Re: York (YK FK FL P9-CZFS CENTIFUGAL CHILLER)
hi i tend to agree with ice on this sounds like a eprom problem check rtc chip .
is this a millennium controller?
if so replace display!!!! as u allready changed all else.
-
11-11-2009, 11:27 AM #8
Re: York (YK FK FL P9-CZFS CENTIFUGAL CHILLER)
Hi,to all check your micro board input voltage from power supply board to j1 (i think)and wire number 301 that voltage must be constant if not re boot will happen try to change the wire harness 12 inch length and solder the pins and try it will solve the probem if not change micro board in to programme card type with lateste version of 307 best of luck
-
11-11-2009, 01:38 PM #9
Re: York (YK FK FL P9-CZFS CENTIFUGAL CHILLER)
Hi,
The Microboard will reboot everytime 5VDC that is supplied by Power supply board drop to 4.7 VDC. There is a regulator inside the Power supply board that controls this voltage. Adjust that so that it maintains 5.2VDC while chiller is OFF.Setrite
A group of Donkey's Led by a Lion can defeat a group of Lion's led by a Donkey
Similar Threads
-
York Chiller problems
By ingherrera in forum CommercialReplies: 18Last Post: 26-07-2011, 03:10 PM -
York Chiller startup when on Emergency Power
By Apollo10 in forum Trouble ShootingReplies: 3Last Post: 22-12-2008, 07:13 PM -
need help on YORK chiller
By nassersh in forum CommercialReplies: 4Last Post: 16-12-2008, 12:47 PM -
york chiller motor rotation error
By cesarnino in forum Trouble ShootingReplies: 7Last Post: 13-12-2008, 03:43 PM -
York Screw Chiller How low will it go?????
By bruceboldy in forum Industrial CompressorsReplies: 11Last Post: 10-08-2007, 10:29 PM