Results 1 to 9 of 9
    wcam3's Avatar
    wcam3 Guest
    Changing length of the evaporating coil
    Dear members,
    I am upgrading my existing cooling unit. Presently the unit has 750 BTU compressor, which I am increasing to 3600 BTU. The evaporating coil is presently of SS, 5/16" (8 mm) dia.
    Coil length is 8 metres
    Evaporating coil temperature is -7 degrees
    The ambient temperature is around 40 degrees
    The condensing temperature is around 55 degrees
    Please suggest by how many times I have to increase the length of the evaporator coil to match the new compressor rating.
    If any one can suggest the method to calculate the length of the evaporator coil based on these parameters, I would be highly obliged
    Thanks and regards
    Giridhar
    PS: The present design is working perfectly.
    70
    10,650
    52
    Re: Changing length of the evaporating coil
    Quote Originally Posted by wcam3 View Post
    So why the change ?
    Mar 2009
    KZN, South Africa
    58
    2,212
    14
    I agree with Brian. Why not rather install a new system in parallel with the existing, perfectly-functioning system? Surely this is a lot less risky?
    wcam3's Avatar
    wcam3 Guest
    Quote Originally Posted by desA View Post
    There is a space constraint to put a parallel system. I plan to replace the present compressor with the new one.
    70
    10,650
    52
    I repeat the question, why?
    Split Croatia
    52
    6,108
    30
    You cannot replace compressor and evaporator only. You need to match every component of system, therefore you cannot done that by changing parts of system. Especially not by 5 times increase in capacity!
    Forget about that!
    Mar 2009
    South Africa
    43
    As per above...
    You need to change the following:
    Compressor
    Condenser
    Evaporator
    Condenser fans
    Evap fans
    All piping
    All valves
    Distributor
    Expansion valve
    Liquid receiver
    Suction accumulator
    Mar 2009
    32
    i also strongly recomend changing electrical cables so you dont overload the one you have
    Oct 2005
    IRAN
    48
    892
    13
    Hi there,
    Everything said perfectly by others.
    Increasing compressor power means increasing everything else like mentioned above.
    I suggest you think again before making such changes.
    Even Einstein Asked Questions
  1. How to calculate the length of evaporator coil
    By wcam3 in forum Technical Discussions
    Last Post: 06-08-2008, 12:52 PM
  2. Coil Length calculation for de-humidifier
    By gvkindia in forum Tools and Calculators
    Last Post: 31-07-2007, 10:42 PM
  3. Dont be shy, advice needed.
    By Sledge in forum Air Conditioning
    Last Post: 27-06-2007, 03:09 PM
  4. DX coil distributor issue
    Last Post: 16-11-2005, 01:03 PM
  5. Article in ACH&R News
    By Gary in forum Fundamentals
    Last Post: 20-05-2003, 12:27 AM