    Hitachi RAM-18CZ1 Outdoor unit



    I have been asked to re-install one Ram18 to 2 RAS9's.(an old r22 system)
    By looking at the electrical connections, it appeares that the outdoor unit has each of its compressors fed by a 13 amp supply from the indoor unit.
    Sorry if this is a daft question, but i havn't seen it done like this before.
    Is this correct ?
    If so, and they are totally independant circuits, do you have simultaneous haeting and cooling ?

    The RAM-30 CW1 that is the same age and also needs re-installing, has the more conventional 30a to outdoors, then powered interconnections.

    Am i missing somthing ?

    cheers

    eggs



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Hitachi RAM-18CZ1 Outdoor unit

    Hi eggs.

    Is it a split unit with one condensing unit and one evaporator?

    Chemi

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Hitachi RAM-18CZ1 Outdoor unit

    Hi eggs.

    Found this link, might be helpful
    http://www.hitachi-hk.com.hk/FileMan...er/air_con.pdf
    Chemi

  4. #4
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    745
    Rep Power
    25

    Re: Hitachi RAM-18CZ1 Outdoor unit

    Hi chemi.
    it is a multi split, with 2 indoors to one outdoor.
    cheers

    eggs

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Hitachi RAM-18CZ1 Outdoor unit

    Ok eggs.

    Usualy there are two compressors in the outdoor unit.

    and the power supply is also to the outdoor unit.

    In that case, you can have one unit cooling and the other on heating mode. Very simple and basic.

    Chemi

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Hitachi RAM-18CZ1 Outdoor unit

    Hi eggs.

    Very sorry about that link, just realized its in Chinese.

    I'll try to find a better one.

    Chemi

  7. #7
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Hitachi RAM-18CZ1 Outdoor unit


  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Hitachi RAM-18CZ1 Outdoor unit

    In that case, you can have one unit cooling and the other on heating mode. Very simple and basic.
    I don't see any reversing valves on the schematic Chemi - it looks like a cooling only system

  9. #9
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Hitachi RAM-18CZ1 Outdoor unit

    Hi Frank.

    I guess you are right.
    I didnt all the pages, it would take me ages to download it.
    My connection is not very fast, more of giving eggs the idea of what it is .

    Chemi

  10. #10
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Hitachi RAM-18CZ1 Outdoor unit

    By looking at the electrical connections, it appeares that the outdoor unit has each of its compressors fed by a 13 amp supply from the indoor unit.
    This is a very common way of doing it Eggs - most of the old Marstair, Qualitaire etc. units do it this way. Basically the mains is fed from the outdoor to power the indoor fan then a switched live feeds back out to run the compressor through the stat/relay. The MCU range of IMI condensing units still does it this way.

    If so, and they are totally independant circuits, do you have simultaneous haeting and cooling ?
    If you had reversing valves and seperate condensers then yes but this unit has a shared condenser and is cooling only

Similar Threads

  1. Hitachi Air-con Problem
    By oddjob in forum Air Conditioning
    Replies: 10
    Last Post: 12-05-2008, 01:46 AM
  2. Hitachi Details
    By Slim R410a in forum Air Conditioning
    Replies: 4
    Last Post: 29-06-2006, 10:20 AM
  3. hitachi utopia g7 r404a not up to cooling
    By peter1927 in forum Trouble Shooting
    Replies: 12
    Last Post: 16-01-2006, 04:19 AM
  4. F**K Hitachi
    By rbartlett in forum Air Conditioning
    Replies: 38
    Last Post: 24-10-2005, 05:12 PM
  5. Hitachi central controller
    By al in forum Air Conditioning
    Replies: 5
    Last Post: 28-09-2005, 07:55 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •