Results 1 to 14 of 14
  1. #1
    Join Date
    Aug 2009
    Location
    US
    Posts
    7
    Rep Power
    0

    A/C basic questions:



    -The temperatures and PSIG are applied to all A/C that ask for R22 even with different tons capacity?


    -What is the relationship between the length of the lines and temperatures and PSIG?


    -If outside temp is over 95F. How the condense is cooling the liquid?


    -If A/C has low *****, can a tech determine how many lbs is need by just checking the manifold gauge? How can it be done by going by the PSIG?


    -How can I find out the temperature for superheat and sub cooling is right? Is it different for each coolant?
    Thanks Carlos



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: A/C basic questions:

    Quote Originally Posted by cralx2k View Post
    -The temperatures and PSIG are applied to all A/C that ask for R22 even with different tons capacity?
    All gases has relation between temperature and pressures. Question is not logical. Rephrase.


    -What is the relationship between the length of the lines and temperatures and PSIG?
    Same as above! Longer the lines, pressure drop is higher, saturation temperature changes. We need some context for meaningful answer.


    -If outside temp is over 95F. How the condense is cooling the liquid?
    If gas entering condenser is at 120°F and air entering condenser is 95°F than, at right pressures, that gas could change state to liquid (condense) at say 100°C without problem.
    Check at Google "Saturation pressure" and "latent energy".
    In refrigeration, everything is connected with change of state of matter (refrigerant) from gas to liquid and vice-verse.


    -If A/C has low *****, can a tech determine how many lbs is need by just checking the manifold gauge?
    No!

    How can it be done by going by the PSIG?
    It cannot be done! More information's needed and still cannot be determined how many! It only could be determined if it is short of refrigerant or overcharged but amount in lbs stays enigma.
    Check link supplied by Gary.


    -How can I find out the temperature for superheat and sub cooling is right?
    Check link supplied by Gary.

  4. #4
    Join Date
    Aug 2009
    Location
    US
    Posts
    7
    Rep Power
    0

    Re: A/C basic questions:

    Thanks Gary, great info. Where I can buy your book?

  5. #5
    Join Date
    Aug 2009
    Location
    US
    Posts
    7
    Rep Power
    0

    Re: A/C basic questions:

    Thanks for the reply nike123. I just started my HVAC education. My questions were about what I’m studying and the last A/C repair in my home.
    I have the “Refrigerating & Air Conditioning Technology 5th Edition as a text book. I understand a typical air-conditioning system temp, pressure and airflow. Let me try to rephrase my question.
    If I don’t have any manufacturer parameters that the unit should optimally be running and I know only:
    Evap air in temp
    Evap air out temp
    Low side pressure
    Suction line temp

    Cond air in temp
    Cond air out temp
    High side pressure
    Liquid line temp


    -After calculating the Superheat and/or Sub cooling, how do I know that values are acceptable?
    Low charge? Over charge? Etc

    How do I know how many lbs I need to add if the system is low charge or remove if the system is over charge?

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: A/C basic questions:

    Quote Originally Posted by cralx2k View Post
    Thanks Gary, great info. Where I can buy your book?
    My website is currently out of service as I am in the process of switching servers. I hope to have it up and running again soon... until then it seems I am out of business.

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: A/C basic questions:

    Quote Originally Posted by cralx2k View Post
    How do I know how many lbs I need to add if the system is low charge or remove if the system is over charge?
    You need to recover refrigerant from unit, weigh recovered amount and compare that with unit nameplate where refrigerant amount is stated. If your line-set is exceeding length for which unit is pre-charged, you need to add to that additional amount specified in instalation manual of that unit.
    If your weighed amount is different from that, you need to leak test unit to find leak and fix it. After that you need to pressure test unit with dry nitrogen to see if test pressure hold for 12-24 hours (note temperature before and after test, pressure could change at rate of 0,1Bar/1°C).
    After you should evacuate to 500microns vacuum (at least 30 min) and than weigh in accurate amount of refrigerant.

    That is only proper way to know how much lbs of refrigerant you should add or remove.

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: A/C basic questions:

    Quote Originally Posted by cralx2k View Post
    Thanks for the reply nike123. I just started my HVAC education. My questions were about what I’m studying and the last A/C repair in my home.
    I have the “Refrigerating & Air Conditioning Technology 5th Edition as a text book. I understand a typical air-conditioning system temp, pressure and airflow. Let me try to rephrase my question.
    If I don’t have any manufacturer parameters that the unit should optimally be running and I know only:
    Evap air in temp
    Evap air out temp
    Low side pressure
    Suction line temp

    Cond air in temp
    Cond air out temp
    High side pressure
    Liquid line temp


    -After calculating the Superheat and/or Sub cooling, how do I know that values are acceptable?
    Low charge? Over charge? Etc
    Read this article and then ask more questions!

  9. #9
    Join Date
    Aug 2009
    Location
    US
    Posts
    7
    Rep Power
    0

    Re: A/C basic questions:

    Quote Originally Posted by nike123 View Post
    You need to recover refrigerant from unit, weigh recovered amount and compare that with unit nameplate where refrigerant amount is stated. If your line-set is exceeding length for which unit is pre-charged, you need to add to that additional amount specified in instalation manual of that unit.
    If your weighed amount is different from that, you need to leak test unit to find leak and fix it. After that you need to pressure test unit with dry nitrogen to see if test pressure hold for 12-24 hours (note temperature before and after test, pressure could change at rate of 0,1Bar/1°C).
    After you should evacuate to 500microns vacuum (at least 30 min) and than weigh in accurate amount of refrigerant.

    That is only proper way to know how much lbs of refrigerant you should add or remove.
    Thank you for your professional response. I really appreciated.

  10. #10
    Join Date
    Aug 2009
    Location
    US
    Posts
    7
    Rep Power
    0

    Re: A/C basic questions:

    Quote Originally Posted by nike123 View Post
    Read this article and then ask more questions!

    I'll check this out and I'll let you know. Thanks again.

  11. #11
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: A/C basic questions:

    Quote Originally Posted by cralx2k View Post
    Thanks Gary, great info. Where I can buy your book?

    Quote Originally Posted by Gary View Post
    My website is currently out of service as I am in the process of switching servers. I hope to have it up and running again soon... until then it seems I am out of business.
    Good news. I am back in business:

    http://prostores1.carrierzone.com/se...com/StoreFront

  12. #12
    Join Date
    Aug 2009
    Location
    US
    Posts
    7
    Rep Power
    0

    Re: A/C basic questions:

    Check your e-mail.

  13. #13
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: A/C basic questions:

    Quote Originally Posted by cralx2k View Post
    Check your e-mail.
    Got it... thanks.

  14. #14
    pjkflat's Avatar
    pjkflat Guest

    Re: A/C basic questions:

    98 subaru 2.5 outback ac just gets cold t hen off duct emp hits 45 f

Similar Threads

  1. Please help with these questions!!
    By tsl001 in forum Supermarket Refrigeration
    Replies: 31
    Last Post: 05-05-2010, 11:19 AM
  2. Basic Questions about AC
    By goulbourne in forum Training
    Replies: 3
    Last Post: 19-03-2009, 01:40 PM
  3. Interview questions
    By zimbo in forum Chit Chat & Service Stories
    Replies: 16
    Last Post: 10-09-2008, 10:06 PM
  4. A couple of questions.
    By marc5180 in forum Fundamentals
    Replies: 10
    Last Post: 05-03-2008, 01:04 AM
  5. questions
    By parry in forum Chit Chat & Service Stories
    Replies: 17
    Last Post: 31-10-2005, 08:46 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •