19XL High Discharge Temp intermittent alarm at compressor start
The carrier chiller model 19XL5353304CR S/N 1994Jxxxxxx has an intermittent alarm.
The alarm message in alarm history is
'CMPD 221.0 F exceeds limit of 220.0 F, Check Discharge Temperature'.
The intermittent alarm only occurs within 1 min. of compressor start.
The discharge temp display on LID equals to actual compressor discharge temperature measured by thermometer.
(ie., the sensor has no problem.)
From observation, the discharge temp goes from 120 F at compressor start
to sometimes 180 F after 30 sec. from compressor start and drop to 130 F after 1 min from
compressor start. And it is at 115 F (15 F Discharge superheat). This chiller will continue
running until normal shutdown.
In case of alarm, the discharge temp goes from 120 F to 220 F trip point less than 1 min after
compressor start.
The operating condition is
Ent. Chilled water temp 53 F
Lvg. Chilled water temp 42 F (42 F setpoint) (If it continues running)
Evap Refrig Temp 40.3 F
Ent. Cond water temp 86 F
Lvg. Cond water temp 94.8 F (If it continues running)
Cond Refrig Temp 99.6 F
Oil Pressure 29.8 psi
Oil temp 121.7 F
% motor amps 101
The PSIO software part# CESR-500048-08 (version 8).
Any suggestion to correct this problem?
Are there any Carrier service bulletin address this issue?
-
29-08-2009, 10:08 PM #2
Re: 19XL High Discharge Temp intermittent alarm at compressor start
Sightglass clear?
Subcooling temp?
Superheat temp?
-
30-08-2009, 08:50 AM #3
Re: 19XL High Discharge Temp intermittent alarm at compressor start
water temperature in let condenser required 32.c,then its ok after u should be check oil tempetratur nearly required 50c and oil flow
-
30-08-2009, 08:51 AM #4
Re: 19XL High Discharge Temp intermittent alarm at compressor start
Hi Pete, I have worked on centrifs years ago what bothers me is the short time it takes to trip on high discharge temp. Question 1 are the vanes opening to let refrigerant through and what is the amperage at this stage.
NormMy wife used to say you never listen to a word I say at least I think that what she said
-
30-08-2009, 09:02 AM #5
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
08-11-2009, 05:10 PM #6
Re: 19XL High Discharge Temp intermittent alarm at compressor start
differential saturated condenser temperature and condenser water outlet is high cleaning reviews condenser connections implies a falsification of the sensors can give erroneous readings at boot time, give complete readings of the machine and the configuration the same
Similar Threads
-
High Temp Heat Pumps
By US Iceman in forum Heat PumpsReplies: 68Last Post: 29-05-2011, 05:19 PM -
Carrier 23xl chiller-Low discharge superheat alarms
By Bradysmill in forum Trouble ShootingReplies: 7Last Post: 25-04-2010, 07:43 PM -
R406a for high temp heat pump
By Lc_shi in forum RefrigerantsReplies: 1Last Post: 14-10-2005, 09:08 PM -
GSHP discharge temp high
By Lc_shi in forum Trouble ShootingReplies: 6Last Post: 20-01-2005, 08:37 AM -
Disharge temp
By reggie in forum FundamentalsReplies: 4Last Post: 12-09-2002, 05:41 PM