Thread: EXV Hunting
    Jun 2008
    singapore
    41
    34
    EXV Hunting
    Dear all,
    I am using electronic expansion valve on my 15 kW scroll machine and it was running perfectly fine. Recently there was a small leak and i corrected it. After topping up some gas to counter the leak, my system was never stable and the super heat hunts between 3 to 6 deg K compared to earlier fluctuation which is less than 1 K.
    Some one advice me that i should entirely evacuate the system and the recharge it to original charge level.
    Even after that, my superheat still hunts. What could be the problem?
    In between, i also would like to know more on the electronic expansion valve, mainly on the operating principles of the valve. I have found some info on the internet but not much technical explanations. Any sort of information is very much appreciated. I am using Emerson EX 2 together with the accompanied controller
    Please help.
    Regards,
    jaya
    11,024
    Re: EXV Hunting
    Split Croatia
    57
    6,151
    36
    Re: EXV Hunting
    Check that during previous work on system you did not move/damaged/disconnected/etc.. sensors of valve controller.
    Also check parameters on valve controller.
    BTW what is valve controller model # ?
    Also, what is your subcooling?
    Jun 2008
    singapore
    41
    34
    Re: EXV Hunting
    I have reset the controller to the factory setting and then set them according to my specifications. I have also check the mounting of the sensor and other wirings. they all look ok to me.
    About the controller i am using Emerson EC2-391 with EX2 valve.
    My subcooling has been the same all the while approximately 1K
    Split Croatia
    57
    6,151
    36
    Re: EXV Hunting
    Quote Originally Posted by jayaeros View Post
    That subcooling is low!
    If we presume some errors in reading of instruments, it could be easy that you don't have 100% liquid at EXV entrance. That lead to bad superheat control.
    I would add charge until 4-5K subcooling and then look how EXV behave.
    But before, you should check condenser air/water flow and if it is clean (delta T). Same goes for evaporator!
    Where did you measured subcooling? Is it affected by air from condenser? Do you have liquid receiver? What kind of system is that?
  1. Hunting Etc.
    By subzero*psia in forum Hobbies
    Last Post: 19-09-2010, 01:40 PM
  2. hunting expansion valve on airedale c/control
    By knight rider in forum Technical Discussions
    Last Post: 10-07-2009, 11:21 PM
  3. TXV hunting in a walkin cooler
    By dkemper in forum Trouble Shooting
    Last Post: 15-11-2007, 03:14 PM
  4. Low System Performance (Hunting ?)
    By rhlg in forum Technical Discussions
    Last Post: 25-10-2006, 01:05 AM
  5. hunting???
    By Friobernal in forum Fundamentals
    Last Post: 18-05-2004, 02:00 PM