    Can't get any sub-cooling



    Hi Guys,

    A 3/4 hp 404A medium temp walkin system rated at about 7500 BTU, @ 90 Ambient.

    So, I realized that my actual ambient is rarely less than 100 degrees, and often hovers in the 110 -115 range. Looking at the charts reduces capacity down to around 3500 BTU at that temp.

    Lots of bubbles in the site glass = NO subcooling.

    Anyhow the thing was adjusted by someone by reducing the refrigerant, 'cuz if you charge it up, we see in excess of 375 PSI liquid line pressure. On occasion the HP Cut out trips.

    To keep SOME cooling, its apparent that the refrigerant was bled off on purpose because of the High ambient. However, low refrigerant means high compressor temps and poor oil flow. Consequestly, the compressor trips off once in awhile.

    Can't install a condenser outside, no place for AC. So, heres the question. Anyone have any ideas on how to go about installing a subcooler? Or maybe the best question is who has something like that for a system this small? Has anyone put in a Sub Cooler of their own making? I was thinking along the lines of something like the variety seen in Manitowoc Ice machines, but that takes a lot of water.

    So there ya go. I didn't add too much in the way of measurements because with a reduced charge, SH is going to be High anyhow, and its obvious there's no SC.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Can't get any sub-cooling

    Is there anything that you can do to increase the airflow over the condenser?

    Can you increase the size of the condenser or fit a second coil?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    dan247's Avatar
    dan247 Guest

    Re: Can't get any sub-cooling

    How bout shade for the unit that's 10-15 degrees cooler right there. And change the condensor fan motor with a higher rpm. Keep them coils clean and make sure there is enough charge for winter time.

  4. #4
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: Can't get any sub-cooling

    Hi Lex, Is there no room to install an exhaust fan

    Norm
    My wife used to say you never listen to a word I say at least I think that what she said

  5. #5
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    55
    Posts
    16
    Rep Power
    0

    Re: Can't get any sub-cooling

    You either need to remove the excess heat from the condensr area, or increase the size of the condenser. I would look at doubling the size at least. The only other thing is a CPR valve to maintain a constant refrigeration effect. You will still only get the 3500btus as the condenser is the limiting factor. If your client doesn't want to spend any money, try winding is the suction valve to maintain a low condensing pressure, or reduce the airflow over the evaporater. Keep in mind these are only patches, not cures.

  6. #6
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Can't get any sub-cooling

    What about a pre-cooler for the air, using the evaporation principle?

    Basically a water pad which raises humidity, but lowers temp into condenser coil? If memory serves, BAC do offer something of this sort. There will be others.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  7. #7
    Join Date
    Mar 2009
    Location
    idaho
    Age
    45
    Posts
    8
    Rep Power
    0

    Re: Can't get any sub-cooling

    you either gotta cool the air in the room or go with a water coax, it may increase the water bill but the equipment will do what it needs to.

Similar Threads

  1. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  2. Energy saving Glycol filled dry cooler circuits
    By Jasper in forum Technical Discussions
    Replies: 14
    Last Post: 19-06-2008, 02:18 PM
  3. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  4. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Industrial
    Replies: 5
    Last Post: 14-10-2005, 06:34 PM
  5. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Fundamentals
    Replies: 0
    Last Post: 13-10-2005, 05:14 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •