Another liquid hammer problem
Hello all
Ive cruised this forum for years, only just joined. Thanks for having me. I work for a company that services and builds scientific refrigeration equipment mostly cascade systems. We recently built a large -30c walk-in. Its a redundant system with 2 seperate refrigeration systems, that cycle every 12 hours. Each condensing unit feeds 2 evaps. 2 evaps on 1 side , 2 on the other. The systems are electric defrost and each system has a subcooler piped so the liquid goes through the subcooler before it feeds the evaps. Each evap has a sv and a txv.
Now my problem is an incredibly severe hammering on 1 of the evaps liquid line. Keep in mind...only 1 evap, on 1 system ... the other system is fine and identical.
We changed both the svs and the txvs, to no avail
When installing these systems we installed a shader valve before the sv for evac and perging. When i hook up my gauges to this shrader the sound goes away. My boss had me, basicly take a piece of 7/8 copper, cap 1 side, and connect it to this shrader. This was several weeks ago and i only recently found out the problem is ocurring once again. I realize that between my hose and gauge, i am allowing a certain amount of expansion and contraction. After reading through your forum im worried my solenoid valves may be too large.
I was thinking an easy fix might be to connect a legth of cap tube to my shrader access and have that feed to an expansion tank, i could easily mount above the cieling. I realize someof you will want specs... you'll have them i the morrow.
thanks for your help. this is driving us crazy!
-
28-08-2009, 01:58 PM #2
Re: Another liquid hammer problem
Hi captaincascade
jsut a thought with the fluid hammer issue you could change the solaniod valve to a motorised version - danfos or something or look at your pipeing layout. If both systems are identicle your pipeing length or bends (charicteristics) would be the only difference.
-
28-08-2009, 09:40 PM #3
-
29-08-2009, 08:00 AM #4
Re: Another liquid hammer problem
Hello. Are there line receivers ?
-
29-08-2009, 08:02 AM #5
Re: Another liquid hammer problem
Of course, there should be - maybe to put a larger one on this particular system ?
-
29-08-2009, 08:18 AM #6
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Another liquid hammer problem
Could you post refrigerant diagram here?
-
29-08-2009, 09:18 AM #7
Re: Another liquid hammer problem
how close is the sv to the exp valve ?
Similar Threads
-
Refrigeration 101
By Gary in forum FundamentalsReplies: 201Last Post: 01-11-2011, 10:18 PM -
Liquid receiver
By Renato RR in forum FundamentalsReplies: 134Last Post: 02-03-2011, 06:55 AM -
Suction gas <-> liquid line heat exchange and performance gains
By DaBit in forum Technical SpeculationsReplies: 30Last Post: 18-05-2010, 01:52 PM -
trouble with liquid return after defrost in rack
By coldkeeper1 in forum Supermarket RefrigerationReplies: 12Last Post: 18-09-2009, 09:46 PM -
Luiquid line vibration and liquid hammer
By Infinity in forum Trouble ShootingReplies: 12Last Post: 09-02-2007, 10:22 PM