    Hello all

    Ive cruised this forum for years, only just joined. Thanks for having me. I work for a company that services and builds scientific refrigeration equipment mostly cascade systems. We recently built a large -30c walk-in. Its a redundant system with 2 seperate refrigeration systems, that cycle every 12 hours. Each condensing unit feeds 2 evaps. 2 evaps on 1 side , 2 on the other. The systems are electric defrost and each system has a subcooler piped so the liquid goes through the subcooler before it feeds the evaps. Each evap has a sv and a txv.

    Now my problem is an incredibly severe hammering on 1 of the evaps liquid line. Keep in mind...only 1 evap, on 1 system ... the other system is fine and identical.

    We changed both the svs and the txvs, to no avail

    When installing these systems we installed a shader valve before the sv for evac and perging. When i hook up my gauges to this shrader the sound goes away. My boss had me, basicly take a piece of 7/8 copper, cap 1 side, and connect it to this shrader. This was several weeks ago and i only recently found out the problem is ocurring once again. I realize that between my hose and gauge, i am allowing a certain amount of expansion and contraction. After reading through your forum im worried my solenoid valves may be too large.

    I was thinking an easy fix might be to connect a legth of cap tube to my shrader access and have that feed to an expansion tank, i could easily mount above the cieling. I realize someof you will want specs... you'll have them i the morrow.

    thanks for your help. this is driving us crazy!



  2. #2
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: Another liquid hammer problem

    Hi captaincascade
    jsut a thought with the fluid hammer issue you could change the solaniod valve to a motorised version - danfos or something or look at your pipeing layout. If both systems are identicle your pipeing length or bends (charicteristics) would be the only difference.

  3. #3
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Another liquid hammer problem

    Quote Originally Posted by captaincascade View Post
    Hello all

    Ive cruised this forum for years, only just joined. Thanks for having me. I work for a company that services and builds scientific refrigeration equipment mostly cascade systems. We recently built a large -30c walk-in. Its a redundant system with 2 seperate refrigeration systems, that cycle every 12 hours. Each condensing unit feeds 2 evaps. 2 evaps on 1 side , 2 on the other. The systems are electric defrost and each system has a subcooler piped so the liquid goes through the subcooler before it feeds the evaps. Each evap has a sv and a txv.

    Now my problem is an incredibly severe hammering on 1 of the evaps liquid line. Keep in mind...only 1 evap, on 1 system ... the other system is fine and identical.

    We changed both the svs and the txvs, to no avail

    When installing these systems we installed a shader valve before the sv for evac and perging. When i hook up my gauges to this shrader the sound goes away. My boss had me, basicly take a piece of 7/8 copper, cap 1 side, and connect it to this shrader. This was several weeks ago and i only recently found out the problem is ocurring once again. I realize that between my hose and gauge, i am allowing a certain amount of expansion and contraction. After reading through your forum im worried my solenoid valves may be too large.

    I was thinking an easy fix might be to connect a legth of cap tube to my shrader access and have that feed to an expansion tank, i could easily mount above the cieling. I realize someof you will want specs... you'll have them i the morrow.

    thanks for your help. this is driving us crazy!

    Could the shrader be interfering with the flow??

    taz.

    .

  4. #4
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Another liquid hammer problem

    Hello. Are there line receivers ?

  5. #5
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Another liquid hammer problem

    Of course, there should be - maybe to put a larger one on this particular system ?

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Another liquid hammer problem

    Could you post refrigerant diagram here?

  7. #7
    Join Date
    Feb 2007
    Location
    newcastle but now carlisle
    Age
    53
    Posts
    195
    Rep Power
    18

    Re: Another liquid hammer problem

    how close is the sv to the exp valve ?

Similar Threads

  1. Refrigeration 101
    By Gary in forum Fundamentals
    Replies: 201
    Last Post: 01-11-2011, 10:18 PM
  2. Liquid receiver
    By Renato RR in forum Fundamentals
    Replies: 134
    Last Post: 02-03-2011, 06:55 AM
  3. Suction gas <-> liquid line heat exchange and performance gains
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 18-05-2010, 01:52 PM
  4. trouble with liquid return after defrost in rack
    By coldkeeper1 in forum Supermarket Refrigeration
    Replies: 12
    Last Post: 18-09-2009, 09:46 PM
  5. Luiquid line vibration and liquid hammer
    By Infinity in forum Trouble Shooting
    Replies: 12
    Last Post: 09-02-2007, 10:22 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •