    How much cooling do i need?



    Hi everyone,
    I need to know how much cooling I need to cool 7500 pounds per hour of cookies from 120 degrees f to 80 degrees f. I have a conveyor running 32 feet per minute and I don't need to remove any humidity, but if I do it's ok. They are relatively dry anyways. I have a space of 30 feet to add a cooling tunnel etc.



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: How much cooling do i need?

    2800 kg/h x 2.93 kJ/kg.K x 25 K = 20500 KJ/h = +/- 57 kW + fans + losses = +/- 60 kW.

    Then, 2800 kg/h at a speed of 10 m/min gives +/-4.5 kg/m belt. It seems that the cookies will be stacked on each other in a thick layer.

    If you can do this at your belt speed and given length can only be said after a practical trial. Theoretical calculation is one thin, practical feasibility is another thing.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  2. Energy saving Glycol filled dry cooler circuits
    By Jasper in forum Technical Discussions
    Replies: 14
    Last Post: 19-06-2008, 02:18 PM
  3. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  4. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Industrial
    Replies: 5
    Last Post: 14-10-2005, 06:34 PM
  5. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Fundamentals
    Replies: 0
    Last Post: 13-10-2005, 05:14 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •