    copper infection?

    Last I've had a client running his 2008 altherma in cooling mode. The thing went fine until last week, suddenly wasn't able to reach watertemps lover than 19°C.
    Went over there, SH 22°!!!
    Reclaimed refrigerant -> 0,9kg instead of the stock filled 3,7kg!

    Pressure tested the unit and found a leak in the 5/8" suction line about 40cm away from the indoor unit.
    It was a quite large hole in a bent with a radius of about 20cm (slow), nothing special...

    I'm a bit shocked that this could happen to a copper line installed about 1 yr ago!?!

    Did anyone come across this? I'm standing a little negative regarding the copper used and I'm wondering what brand of insulated copper you guys often use?

    Are the twin tubes from armaflex, inoac, ...any good or did someone had a problem like this with any of these?

    kind regards
    Last edited by majo; 27-08-2009 at 10:06 PM.

Similar Threads

  1. Replies: 39
    Last Post: 04-09-2009, 12:16 AM
  2. Use of Copper Fittings
    By Waqas Ahmad in forum Air Conditioning
    Replies: 2
    Last Post: 13-07-2009, 04:33 AM
  3. copper theft?
    By hillbillywillie in forum Chit Chat & Service Stories
    Replies: 6
    Last Post: 20-01-2009, 07:13 PM
  4. joining copper to copper, joining copper to brass
    By mac_J in forum Technical Discussions
    Replies: 9
    Last Post: 15-01-2008, 02:29 AM
  5. Copper tube degreasing specification
    By Thermatech in forum Technical Discussions
    Replies: 2
    Last Post: 23-05-2007, 03:10 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •