    Insolation of horizontal Tank



    Dear Friends

    How should be insolated the saddle of a horinzoltal tank (ammoniac separator) which will work at -35ēC.??

    The tank´s volumen is 10 m3

    The application is even worst because the zone where the tank will be located is a very sismic .

    We want to suggest polyuretane 40 kg/m3

    Thanks for yours comments
    Regards
    Gwapa



  2. #2
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Insolation of horizontal Tank

    You can use a saddle with a thermal break such as Oak wood or a plastic to rest the vessel on. Several ways to do this.

    Or you can make the legs longer and insulate down the legs.

    Ken

  3. #3
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: Insolation of horizontal Tank

    Thanks TXiceman
    I am plannig to use hi density poliuretane 200kg/m3 for themal break but how do we tie the tank to evoid movements in a ismic situation?
    Gwapa

Similar Threads

  1. Atmospheric Storage of Ammonia
    By asif in forum NH3
    Replies: 15
    Last Post: 24-06-2009, 05:16 AM
  2. Co2 Tank refrigeration system
    By Prashant Kumar in forum CO2
    Replies: 7
    Last Post: 24-04-2009, 07:55 PM
  3. Recovery tank
    By dddon in forum Chit Chat & Service Stories
    Replies: 5
    Last Post: 01-12-2008, 02:53 AM
  4. Bypass buffer tank volume
    By abbasi in forum Technical Speculations
    Replies: 3
    Last Post: 15-10-2008, 05:28 AM
  5. How an expansion tank works?
    By Raadster in forum Fundamentals
    Replies: 6
    Last Post: 25-07-2008, 02:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •