    Comparison of R22 vs 407C on water chiller



    Hi, I'm mainly familiar with R22 in water chillers. I understand 407C is similar in terms of running pressures, temperatures etc. I'm looking at a water cooled chiller and I'm getting 18 - 19 bar head pressure and 3.5 - 3.8 bar suction at 18 degC ambient. I would assume if this was 22 that the condenser is fouled or we have a problem with the dry air cooler on the roof but I just want to confirm my assumption that the head pressure should be no higher than about 12 - 14bar. Also looking at some of the other threads on 407c it seems that at higher condensing temps it may run into trouble cooling, any thoughts? Its a shell and tube HX by the way. Chiller is about 10 years old.
    Fintan



  2. #2
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Comparison of R22 vs 407C on water chiller

    Fintan

    12 to 14 would be right if you had eev's fitted, for tev's i'd be running at 16 to 18b, this is assuming leaving water temps of about 6c. Pressures for 407 and 22 are similar except evaporating at zero 22 would be 4b and 407 would be slightly higher.

    Post more info on the chiller operating conditions, lwt,ewt ambient, air off etc....

    al

  3. #3
    Fintanlyons's Avatar
    Fintanlyons Guest

    Re: Comparison of R22 vs 407C on water chiller

    Thanks AL
    One system
    TEVs are fitted, screw compressors (one per circuit X2). Remote DX condenser on 407C.
    3.5 bar suction
    19Bar discharge
    ambient 18degC
    Evap inlet water temp 10degC
    Evap outliet water temp 8deg C
    Sight glass clear
    50amps at 420v (high side) expected 400
    FL

  4. #4
    Alfred85's Avatar
    Alfred85 Guest

    Re: Comparison of R22 vs 407C on water chiller

    Hi, i m new guy here and i m a undergraduate student. i m doing a reserch abt absorption refrigeration system. the system that i use is Gas Absorption Refrigeration Unit (Model: RF 10) which consist of ammonia,water and a bit gas hydrogen. Do anyone know that wat is the pressure in this system? and hw i wan to calculate the exergy because i dont have the data of mass flow rate.. what i have is the temperature of boiler, condenser, evaporator and absorber..

  5. #5
    samirdafadar's Avatar
    samirdafadar Guest

    Re: Comparison of R22 vs 407C on water chiller

    What is the Cu tube size of Ref. piping of PAHU unit 21 TR?

Similar Threads

  1. small water chiller with blocked tubes
    By multisync in forum Air Conditioning
    Replies: 6
    Last Post: 11-06-2009, 03:07 PM
  2. pure water from air
    By Lc_shi in forum New Technologies
    Replies: 32
    Last Post: 26-02-2009, 12:25 PM
  3. Water Chiller
    By lana in forum Technical Speculations
    Replies: 20
    Last Post: 23-06-2007, 01:19 AM
  4. Connecting Trane Water chiller to air handling unit
    By celtictech in forum Fundamentals
    Replies: 10
    Last Post: 08-03-2007, 06:14 PM
  5. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •