    Freezer temp. control without thermostat.



    This is my first question. I am new in HVAC and not good English. Sorry if using wrong English.

    My old freezer (More than 10 yrs) have 2 tons compressor but TXV was only 1 ton (I don't know why) running without thermostat. The temperature was controled by dual pressure controller at condensing unit. Freezer room size is around 5' x 8' x 7'.

    Now I need to change the TXV because the superheat is very high.(About 20 degree F) My question is "Can I change to 2 tons TXV?"

    Thanks,
    Sukitlek.



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Freezer temp. control without thermostat.

    More system information required, pressures and pipe run lengths. TEV are based on pressure drop across vav, for actual capacity performance, do not just read labels.
    magoo

  3. #3
    sukitlek's Avatar
    sukitlek Guest

    Re: Freezer temp. control without thermostat.

    The condensing unit locate on the top of freezer then the pipe is not so long (less than 15'),
    - The pressure between receiver tank and dryer is between 300-320 psig.
    - suction of compressor is between 30-40 psig.
    - suction line temp. more than 35

    Last year the freezer worked OK about 20 F. But now temp. higher to 30 F., I cleaned TXV. (strainer and valve). During operating, Ice accumulate after TXV. at expand pipe from 1 tube to small many tube (about 3 inches after TXV.)

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Freezer temp. control without thermostat.

    Quote Originally Posted by sukitlek View Post
    The condensing unit locate on the top of freezer then the pipe is not so long (less than 15'),
    - The pressure between receiver tank and dryer is between 300-320 psig.
    - suction of compressor is between 30-40 psig.
    - suction line temp. more than 35

    Last year the freezer worked OK about 20 F. But now temp. higher to 30 F., I cleaned TXV. (strainer and valve). During operating, Ice accumulate after TXV. at expand pipe from 1 tube to small many tube (about 3 inches after TXV.)
    What refrigerant?

    How much subcooling you have at receiver outlet? Any sight glass?

    What is compressor model#?
    What is TXV model#?
    What is evaporator model#?
    Pipes dimensions and equivalent lengths.
    Height difference?

    If your freezer worked OK and now it doesn't, than some problem is developed with its operation or you changed heat load.
    MY first guess is: TXV bulb is lost its charge if subcooling is good.
    Last edited by nike123; 23-08-2009 at 09:10 AM.

  5. #5
    Join Date
    Aug 2009
    Location
    Turhona.libya
    Posts
    79
    Rep Power
    15

    Re: Freezer temp. control without thermostat.

    Dual pressure switch is usually the control method in walk_ins freezers. There is a thermostat which controls the solenoid valve.unless i know the refrigerant you are using it's very hard to guess correctly

  6. #6
    Join Date
    Aug 2009
    Location
    Turhona.libya
    Posts
    79
    Rep Power
    15

    Re: Freezer temp. control without thermostat.

    Dual pressure switch is usually the control method in walk_ins freezers. There is a thermostat which controls the solenoid valve.unless i know the refrigerant you are using it's very hard to make a correct guess.

  7. #7
    sukitlek's Avatar
    sukitlek Guest

    Re: Freezer temp. control without thermostat.

    Thank you and Sorry for less information.
    - Compressor model is Copeland CRD1-0206-PFV-970 (Old model and equivalent to CR24KQ-PFV-980WB)
    - TXV Sporlan QE-3/8x1/2x1/4 SAE-QC-2-KT-43-VZ
    - The refrigerant is R22.
    - Ambient Temp. 75-95 F for now

    If the dual pressure switch is usually to cnotrol. I decide not change TXV to 2 tons and still change to 1 ton (The same old one). But after renew TXV. I would like to know, How much setting point the dual pressure controller, for High side, Low side and differrent setting.
    I understand that low side use for temp. control in freezer room, High side to protect the compressor and diff. pressure for how long the commpressor restart, am I right?

  8. #8
    Join Date
    Mar 2008
    Location
    England
    Posts
    232
    Rep Power
    20

    Re: Freezer temp. control without thermostat.

    This is like the old days and I mean 40 plus years ago, I was with Frigidaire and most systems had only control via LP switch, even in what were then considered to be super markets.
    As an example we would set 38/42F applications to operate with a cut out pressure of 15psig and cut in at 33psig this gave off cycle defrost as well as temperature control.
    I can't help feeling that progress does not always result in better or for that matter more economical products, some times just more complicated and more expensive. The KISS principle is still in my view the best route to reliability in most products

  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Freezer temp. control without thermostat.

    Quote Originally Posted by nike123 View Post

    How much subcooling you have at receiver outlet? Any sight glass?

    ...................................

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Freezer temp. control without thermostat.

    Quote Originally Posted by sukitlek View Post
    Thank you and Sorry for less information.
    - Compressor model is Copeland CRD1-0206-PFV-970 (Old model and equivalent to CR24KQ-PFV-980WB)
    - TXV Sporlan QE-3/8x1/2x1/4 SAE-QC-2-KT-43-VZ
    - The refrigerant is R22.
    - Ambient Temp. 75-95 F for now
    I am not aware of any CRD1 compressor with 0206 designation. It should be CRD1-0200-PFV......

    That compressor is designed for high temperature applications or air conditioning and freezer is not his intended use. He cannot go below 0°F evaporation temperature (around 20°F box temperature). His capacity is 12500 BTU/Hr at 20°F/120°F evaporation/condensing (7070 Btu/hr at 0°F/110°F evaporation/condensing).


    yI6sEOesJuPPtRjYWVFHd1I90OPICSummary.pdf

    You should stick with that TXV since it is matched to your compressor capacity at freezer temperatures.
    You could only change thermostatic element (after you prove that is faulty).
    Last edited by nike123; 23-08-2009 at 06:42 PM.

  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Freezer temp. control without thermostat.

    Quote Originally Posted by sukitlek View Post
    I would like to know, How much setting point the dual pressure controller, for High side, Low side and differrent setting.
    I understand that low side use for temp. control in freezer room, High side to protect the compressor and diff. pressure for how long the commpressor restart, am I right?
    Yes, you are right.

    Settings:
    http://sporlan.jandrewschoen.com/Col...ng%20Guide.pdf

  12. #12
    Join Date
    Aug 2009
    Location
    Turhona.libya
    Posts
    79
    Rep Power
    15

    Re: Freezer temp. control without thermostat.

    Wireless maintenance never give good results in your situation. It's better if you get the help of the one who made you learnt mechanical refrigeration

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Freezer temp. control without thermostat.

    Quote Originally Posted by sukitlek View Post

    Last year the freezer worked OK about 20 F. But now temp. higher to 30 F.
    20°F for freezer is not good temperature. What goods are inside?

  14. #14
    sukitlek's Avatar
    sukitlek Guest

    Re: Freezer temp. control without thermostat.

    Thank you very very... much Nike123.
    The system have no sight glass. The subcool I did not check yet cause of no good temp. measuring device.(I just the one that interest in HVAC, Not a technician just DIY and just class I hvac certificate in FL. USA., But I will purchase the temp. measuring device tomorrow with new TXV).
    - The freezer use for chicken breast and that temp.(20F) is good for slide the breast. If too cool it very hard to slide.

    Thank you again. Nike123

  15. #15
    Join Date
    Aug 2009
    Location
    UNITED STATES
    Age
    65
    Posts
    19
    Rep Power
    0

    Re: Freezer temp. control without thermostat.

    Sir,
    i would go back to 1 ton txv and recheck the settings on the low pressure control

Similar Threads

  1. Bosch Fridge Freezer Control Panel Problem
    By Bork in forum Domestic
    Replies: 1
    Last Post: 25-08-2009, 01:02 AM
  2. Ultra low Temp Freezer Design
    By jwasir in forum Fundamentals
    Replies: 27
    Last Post: 18-12-2008, 06:56 PM
  3. Hotpoint FFA71 Freezer High Temp Light / Fridge is Freezing
    By sumnerpa in forum Trouble Shooting
    Replies: 1
    Last Post: 19-08-2008, 03:16 PM
  4. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  5. lowering freezer temp ?
    By knighty in forum Industrial
    Replies: 16
    Last Post: 18-08-2006, 06:24 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •