    burst pipework explosion with pics



    My boss has emailed me pics of a coil that has exploded at 1 of our sites in England.

    The “blown” pipe is in the condenser coil on the discharge side of the compressor, it would appear that the HP switch may have failed and caused the condensing unit to run whilst in a high pressure condition, I would have expected the compressor to fail before the pipework, but it is an extremely old system.

    Has anybody any other views / ideas on the cause of this?

    Thanks in advance
    Rob

    The pics :













  2. #2
    Join Date
    Feb 2008
    Location
    Wellingborough
    Age
    56
    Posts
    35
    Rep Power
    0

    Re: burst pipework explosion with pics

    Is there not any safety valves etc?

  3. #3
    Join Date
    May 2005
    Location
    n.ireland
    Age
    54
    Posts
    17
    Rep Power
    0

    Re: burst pipework explosion with pics

    Quote Originally Posted by Tiesse View Post
    Is there not any safety valves etc?
    I havent seen the system myself just a few pics from the boss asking for my opinion as we have a few more similar systems across the estate my company is responsible for maintaining.

  4. #4
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: burst pipework explosion with pics

    This looks like a daikin?

    We have got a couple of these and the motor frams is very poor and distorts. This leads to the belts shredding and either going very loose or shedding completely.

    I have seen loads and loads of systems running without condenser cooling -either from the above or a faulty fan motor etc- and not seen an 'explosion' like that. Most compressors would usually lift their internal release valve before then.

    The first picture looks like it's been kicked in rather than blown out.
    Last edited by multisync; 22-08-2009 at 07:56 AM.

  5. #5
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: burst pipework explosion with pics



    What was this attached to?
    What refrigerant was in the system?
    The piping looks pretty thin-walled...
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  6. #6
    Join Date
    Aug 2009
    Location
    Turhona.libya
    Posts
    79
    Rep Power
    15

    Re: burst pipework explosion with pics

    I don't think a faulty high pressure switch could make refrigeration system ends with an explosion in the event of condenser fan motors failurs.usually compressor relief valve releases the pressure if the pressure increased up to the 450 psi and as compressor temp. getting high the thermall protecter will react to safe the compressor. I would only assume that the said explosion was a result of accessive pressure being put to the system. Like using unregulated nytrogen in the event of pressure leak testing.
    Last edited by Shibhrac; 22-08-2009 at 07:08 PM.

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: burst pipework explosion with pics

    Looks like the end of a spun filter.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: burst pipework explosion with pics

    Looks like more than one safety failed here. Just guessing it was possible that the system was excessivly overcharged. Asides the HP were any other faults found?

  9. #9
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: burst pipework explosion with pics

    Looks like a serious screw-up on someones part, agree with Brian_UK that system overcharged. Possibly installed by a non-refrig tech.

  10. #10
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: burst pipework explosion with pics

    Quote Originally Posted by Brian_UK View Post
    Looks like the end of a spun filter.
    That's what I wondered. This has then torn itself apart, & the pipe has wrapped back to clout the condenser from the outside - hence the external fin damage.

    Mmmhhh...
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  11. #11
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: burst pipework explosion with pics

    When I was much younger and still learning, I was working on a system with a blocked TEV and assumed it was short of gas - so I started putting more and more gas in. Luckily I had high and low gauges fitted. I noticed in about 10 seconds the HP gauge went to the end of the scale. I quickly turned unit off and relieved some pressure from the high side. It was like a hydrostatic pressure build up. Very very lucky. We learn by our mistakes. With the other units on site where the one above had an explosion it would be prudent to remove gas from a few of them to check charge by weight. Also find out ( if overcharged) who did it and educate that person.

  12. #12
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: burst pipework explosion with pics

    I'm guessing here but I suspect it's lost it's gas charge by now so the chances of getting anyone to either admit they did or worse actually know they overcharged it and kept carrying on is unlikely in the extreme.

    I think we need to know at what stage did this happen.Was it during normal operation, without an engineer being present, or during some repairs. More info needed for sure

  13. #13
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: burst pipework explosion with pics

    Someone has been doing hot work in the last picture, maybe they changed the fan motor and damaged the coil in the process, bodged a repair together, and then later the repair blew.

  14. #14
    Join Date
    May 2008
    Location
    England
    Posts
    101
    Rep Power
    16

    Re: burst pipework explosion with pics

    If its on R410 it could be the copper wasn't suitable for the job too.

  15. #15
    Join Date
    Mar 2009
    Location
    ireland
    Posts
    87
    Rep Power
    16

    Re: burst pipework explosion with pics

    i would tend to agree with contactor... last guy at it seems to have hit the condensor also i dont think that unit is designed to be ducted .. there for higher heads etc etc

  16. #16
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: burst pipework explosion with pics

    No way a compressor can burst a pipe on vapour compression. It can only happen for liquid hit or improper nitrogen testing.

  17. #17
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: burst pipework explosion with pics

    Quote Originally Posted by littleyapper View Post
    i would tend to agree with contactor... last guy at it seems to have hit the condensor also i dont think that unit is designed to be ducted .. there for higher heads etc etc
    Why do you think they are not designed for ducting?

Similar Threads

  1. Pipework Flushing
    By frank in forum Air Conditioning
    Replies: 9
    Last Post: 22-08-2009, 07:15 PM
  2. Installing pipework for single split unit
    By electro in forum Air Conditioning
    Replies: 51
    Last Post: 05-03-2009, 06:02 PM
  3. burst pressure standart for 410A
    By cakabo28 in forum Refrigerants
    Replies: 8
    Last Post: 14-02-2008, 06:21 PM
  4. One Dead In McDonald's Air Con Explosion
    By LRAC in forum Air Conditioning
    Replies: 33
    Last Post: 19-09-2007, 01:18 AM
  5. Pipework cleaning up (Inside)
    By Latte in forum Air Conditioning
    Replies: 6
    Last Post: 22-10-2005, 05:55 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •