Results 1 to 12 of 12
    Nov 2009
    united states
    10
    Question environmental chamber
    hi all,
    has anybody ever worked on a pgc climate lab environmental chamber? i realy nead some help
    trouble shooting this one.
    temp set for 60c
    RH set for 90 to 95%
    temp only reaches 55c at best
    RH is ok 90-95
    hot gas bypass all open
    water heater full power on
    air heat --- nothing?
    Aug 2009
    New Zealand
    2,554
    Re: environmental chamber
    Quote Originally Posted by dumbmechanic View Post
    hi all,
    temp set for 60c
    RH is ok 90-95
    I see you are in the US are you really talking about C or do mean F, if you are talking about C turn off the the refrigeration!
    Nov 2009
    united states
    10
    yes celsius. thank you. it may be posible that the hot gas is over loading the heaters. i will look into that. have you ever adjusted the proportional band on one of these?
    Nov 2009
    united states
    10
    watlow control
    micro pro-1000
    mdl# 93-00-03
    Aug 2009
    New Zealand
    2,554
    Never seen one in my Life, but have designed many (but I have come up from the tools back ground)
    The refrigerant is removing your heat
    I presume that the refrigeration is controlled by a humidity controller and the temp is controlled by the heater via some sort of electronic relay/PID controller. It sounds as if this working out of specification.
    To me without knowing the machine I would a temp limit on when the refrigeration runs.
    When you mean water heater, do you mean a steam bath, or a closed loop water heater.
    Nov 2009
    united states
    10
    thank you again your advise is greatly appriciated.
    heating and cooling coils are emersed in water heat exchanger directly in water line going to spray nozzles
    Nov 2009
    united states
    10
    i dont think this would be a closed loop.
    the heaters are in line with the water entering chamber
    Nov 2009
    united states
    10
    wich leads me to think that this heating and cooling cirquit is ok since the relative humidity is in spec.
    Nov 2009
    united states
    10
    what iam now focused on is the air heaters
    i have no power to these. the traic is good. the control board powering these heaters was swapped with the control board for the water cirquit.
    still nothing.
    Aug 2009
    New Zealand
    2,554
    Know we are going down he right track, (sorry I can not help with specifics)
    So from what you have said the problem lies with the power board driver, Have you check all temperature probes (if these are faulty or have moisture damage they can give the impression (to the controller) that the correct temperature has been reached.
    Apart from that it becomes very product dependent!!!!!!
    Nov 2009
    united states
    10
    i checked the probes today- all okay. determined the cause to be with the main power control board. its time to retire the 1985 wattlow 1000. i will be upgrading this one to the 21st century. any sugestions on a reliable control?
    thanks for your help.
    Aug 2009
    New Zealand
    2,554
    In the past I used PLCs, "AB", or Shimiden out of Japan.
    There must be plenty of good gear in the States.
    Is it $ driven? If not go for industrial quality, if price driven Carell seem OK
  1. how to size the flash chamber in a multistage compression system
    By frank721 in forum Technical Discussions
    Last Post: 06-08-2010, 05:13 PM
  2. Enviormental Chamber Question
    By MaxPoon in forum Fundamentals
    Last Post: 25-04-2010, 01:25 AM
  3. Humidity Chamber - Please Help
    By Deejay in forum Technical Discussions
    Last Post: 29-09-2007, 03:17 AM
  4. High Humidity Chamber
    By smpsmp45 in forum NH3
    Last Post: 12-09-2007, 07:25 AM
  5. environmental protection act
    By neil sailes in forum Fundamentals
    Last Post: 11-12-2003, 07:38 PM