    Question environmental chamber



    hi all,
    has anybody ever worked on a pgc climate lab environmental chamber? i realy nead some help
    trouble shooting this one.

    temp set for 60c
    RH set for 90 to 95%
    temp only reaches 55c at best
    RH is ok 90-95

    hot gas bypass all open
    water heater full power on
    air heat --- nothing?



  2. #2
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: environmental chamber

    Quote Originally Posted by dumbmechanic View Post
    hi all,
    has anybody ever worked on a pgc climate lab environmental chamber? i realy nead some help
    trouble shooting this one.

    temp set for 60c
    RH set for 90 to 95%
    temp only reaches 55c at best
    RH is ok 90-95

    hot gas bypass all open
    water heater full power on
    air heat --- nothing?
    I see you are in the US are you really talking about C or do mean F, if you are talking about C turn off the the refrigeration!

  3. #3
    Join Date
    Nov 2009
    Location
    united states
    Age
    41
    Posts
    10
    Rep Power
    0

    Re: environmental chamber

    yes celsius. thank you. it may be posible that the hot gas is over loading the heaters. i will look into that. have you ever adjusted the proportional band on one of these?

  4. #4
    Join Date
    Nov 2009
    Location
    united states
    Age
    41
    Posts
    10
    Rep Power
    0

    Re: environmental chamber

    watlow control
    micro pro-1000
    mdl# 93-00-03

  5. #5
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: environmental chamber

    Never seen one in my Life, but have designed many (but I have come up from the tools back ground)
    The refrigerant is removing your heat
    I presume that the refrigeration is controlled by a humidity controller and the temp is controlled by the heater via some sort of electronic relay/PID controller. It sounds as if this working out of specification.
    To me without knowing the machine I would a temp limit on when the refrigeration runs.
    When you mean water heater, do you mean a steam bath, or a closed loop water heater.

  6. #6
    Join Date
    Nov 2009
    Location
    united states
    Age
    41
    Posts
    10
    Rep Power
    0

    Re: environmental chamber

    thank you again your advise is greatly appriciated.
    heating and cooling coils are emersed in water heat exchanger directly in water line going to spray nozzles

  7. #7
    Join Date
    Nov 2009
    Location
    united states
    Age
    41
    Posts
    10
    Rep Power
    0

    Re: environmental chamber

    i dont think this would be a closed loop.
    the heaters are in line with the water entering chamber

  8. #8
    Join Date
    Nov 2009
    Location
    united states
    Age
    41
    Posts
    10
    Rep Power
    0

    Re: environmental chamber

    wich leads me to think that this heating and cooling cirquit is ok since the relative humidity is in spec.

  9. #9
    Join Date
    Nov 2009
    Location
    united states
    Age
    41
    Posts
    10
    Rep Power
    0

    Re: environmental chamber

    what iam now focused on is the air heaters
    i have no power to these. the traic is good. the control board powering these heaters was swapped with the control board for the water cirquit.

    still nothing.

  10. #10
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: environmental chamber

    Know we are going down he right track, (sorry I can not help with specifics)
    So from what you have said the problem lies with the power board driver, Have you check all temperature probes (if these are faulty or have moisture damage they can give the impression (to the controller) that the correct temperature has been reached.
    Apart from that it becomes very product dependent!!!!!!

  11. #11
    Join Date
    Nov 2009
    Location
    united states
    Age
    41
    Posts
    10
    Rep Power
    0

    Re: environmental chamber

    i checked the probes today- all okay. determined the cause to be with the main power control board. its time to retire the 1985 wattlow 1000. i will be upgrading this one to the 21st century. any sugestions on a reliable control?
    thanks for your help.

  12. #12
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: environmental chamber

    In the past I used PLCs, "AB", or Shimiden out of Japan.
    There must be plenty of good gear in the States.
    Is it $ driven? If not go for industrial quality, if price driven Carell seem OK

Similar Threads

  1. how to size the flash chamber in a multistage compression system
    By frank721 in forum Technical Discussions
    Replies: 8
    Last Post: 06-08-2010, 05:13 PM
  2. Enviormental Chamber Question
    By MaxPoon in forum Fundamentals
    Replies: 11
    Last Post: 25-04-2010, 01:25 AM
  3. Humidity Chamber - Please Help
    By Deejay in forum Technical Discussions
    Replies: 4
    Last Post: 29-09-2007, 03:17 AM
  4. High Humidity Chamber
    By smpsmp45 in forum NH3
    Replies: 7
    Last Post: 12-09-2007, 07:25 AM
  5. environmental protection act
    By neil sailes in forum Fundamentals
    Replies: 2
    Last Post: 11-12-2003, 08:38 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •