    Units WITHOUT condensers



    Hi all,

    Over the last couple of weeks i have come accross a few units WITHOUT visible condensers on the outside (Gram mostly).

    Is there a condenser inside that you can see or what am i missing

    Regards

    Raymond



  2. #2
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Re: Units WITHOUT condensers

    Hi Ray,How you doing?

    Is there a remote condenser Air/water cooled or maybe a skinned condenser Ie in the walls of the cabinet.
    Whats the model number?.

    Best regards Mark

  3. #3
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Units WITHOUT condensers

    Hi Mark,
    units in question today were Gram F150gb single door freezer & a Gram K190 singlr door chiller.

    Discharge pipes on both units go straight into the body, but wasn't interested enough at the time to start taking all the back panels off.

    Thought it was wierd but then again i was at the riverside leisure complex in Norwich so what else should i expect

    Regards

    Raymond

  4. #4
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Re: Units WITHOUT condensers

    Ray, you wouldnt need to take the side cover off just feel the side of the cabinet and see if its warm .

    Mark

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Units WITHOUT condensers

    Condensor tubes are foamed in the walls just near the outher plate and dissipate their heat to the surrounding. If you feel on the steel outher walls, they wil be warm and on some places hot.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Units WITHOUT condensers

    Hi Thanks fo the replies,
    What a stupid idea these are

    They are sold as under counter units and sold for use in kitchens. With an ambient of 30 degree's + and no airflow around them where they are wedged in, it's no wonder they don't work very well

    Regards

    Raymond

  7. #7
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Re: Units WITHOUT condensers

    If i recall ,Gram added a (guarded) tangental type motor,fitted on the back to aid condensing on some of there cabinets....... or was it Derby or something....Still,in that application.

  8. #8
    Join Date
    Mar 2004
    Location
    UK
    Posts
    624
    Rep Power
    21

    Re: Units WITHOUT condensers

    Hi I,ve had trouble with the doors dropping,just enough to stop them sealing properly.The staff use them to aid them back on there feet,the hinges are not strong enough.I agree they are no good for kitchens they work flat out.

    Regards bernard

  9. #9
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Units WITHOUT condensers

    Hi Mark,
    Yes, these units have that fan but when the units are in a recess under a counter with no airspace then whats the point.

    Regards

    Fatboy

  10. #10
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Re: Units WITHOUT condensers

    Quote Originally Posted by MarkFiddy
    If i recall ,Gram added a (guarded) tangental type motor,fitted on the back to aid condensing on some of there cabinets....... or was it Derby or something....Still,in that application.
    Re-read the post.

  11. #11
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Units WITHOUT condensers

    Raymond

    I agree with you entirely!!!
    It is a STUPID design, enclosing the condenser tubes inside the foam

    A lot of Gram fridges have a small tangental motor stuck just below the compressor to keep it cool. These by the way have external condensers, ( I think)

    A lot of commercial kitchens buy these type of fridges, considering the high temps in kitchens, and constant door openings..........I cringe!!

    I would never sell one of these units for a catering requirement

    And yes...........I am back in lovely cool refreshing England...with flowers still in bloom and grass so rich and green.........Im tempted to go munch some!!!!!

    Abe
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

  12. #12
    Join Date
    Jun 2003
    Location
    Bennington, Vermont-USA
    Age
    79
    Posts
    93
    Rep Power
    21

    Re: Units WITHOUT condensers

    The reason you find the condensers in these small freezers buried in the insulation is to keep the cabients from sweating in a humid enviroment.

    In my residential refrigeration days back in the '60s they would put electric heaters in some models along the door moulons to keep them from sweating.

    Mark Fiddy that picture of your little boy is adorable. I just celebrated the 3rd anniversary of my 20th birithday but it seems like only yesterday that my boys were that age.

    The expression on his face seems to be saying," Daddy why did they put the steering wheel on the wrong side of the car?"
    Last edited by benncool; 16-09-2004 at 11:27 PM.
    Essayons

  13. #13
    Join Date
    Mar 2002
    Location
    San Francisco Bay Area
    Posts
    180
    Rep Power
    23

    Re: Units WITHOUT condensers

    Quote Originally Posted by Aiyub
    It is a STUPID design, enclosing the condenser tubes inside the foam

    Abe
    Abe,

    Is it still stupid if it works really well in some applications? If the compressor sees the same condensing pressure, what does it matter how the heat is rejected?

    I don't see how they can be very efficient, with the cooling coil and the condenser coils separated by a couple of inches of foam, but how efficient are all the units operating with plugged condensers because no one ever looks at them?

    The condensing surface is very large and they require the least service of any units. No fan-forced coils to get dirty, just a fan motor to cool the compressor only, so that needs oil every couple of years, but that's it.

    Kelvinator, a quality brand, made ice cream dipping cabinets with the condenser in the walls. I have customers with these units which have run trouble-free for 30 years! They have even covered the fronts with wood veneer and the units don't seem to care!

    Gram is selling thousands of very small units of the same design over here now. Every convenience store has one or two.

    So what are you mad about, really?

    Rog

  14. #14
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Units WITHOUT condensers

    Hi guys.

    I have to agree with Rog.

    We tend to give marks to manufacturers on their products but do we have the right to do so?

    If a product is bad with many problems, it will not sell!

    The "condenser less" freezer is an old trick and manufactures around the world in many versions and they are just fine.
    Of course, if there is a leak inside the body, its gone but it hardly ever happened.

    Chemi

  15. #15
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Units WITHOUT condensers

    Hi Guys,

    I think the problem a lot of the time is misapplication of equipment. How may times have we been called to jobs and it's external factors causing units not to work.

    1) Shops with 15 integrals and no a/c
    2) Kitchens with a 30 degree + ambient
    3) Bars with a long line of integral bottle coolers in a recess under the counter with no air space at the back.

    I will look at the RAC2005 and see what the manufactures say are the operating conditions (if any) of their fridges.
    Clearly these units with the inbuilt condenser are useless in a kitchen enviroment. i know i moan about greasy condensers but at least you can clean them out with grease gobbler and get them working ok'ish.

    Regards

    Fatboy

  16. #16
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Units WITHOUT condensers

    So what are you mad about, really?
    Whos mad ???

    I said it was stupid.................as Fatboy says........there is a tendency to put these units into commercial kitchens.

    15 years ago they worked just fine..............After global warming............we have a whole new scenario here.

    Im referring to the UK..........I cant speak for your neck of the woods.

    Temperatures are much higher here now then was the case, hence the necessity for greater dissipation of heat. With coil embeddded in cabinet, not very practical now.

    And yes, you " DO " get leaks in the condenser coils, I have experienced it several times.

    I prefer external coils, if others prefer internal, great........Ill award you the " sane" medal for your preference
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

  17. #17
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Units WITHOUT condensers

    And who says Manufacturers are the "be all" and " it" who cant get it wrong

    Ive seen many ****ty products in my time, which have sold in the market place successfully.

    Because when it came to servicing the units, the poor tech had to crane his neck, stretch his limbs, and poke fiddle fart about, to get a part changed

    We still get units from reputable manufacturers without charging stubbs fitted............

    In this age of reclaim , I ask ???????
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

  18. #18
    Join Date
    Mar 2002
    Location
    San Francisco Bay Area
    Posts
    180
    Rep Power
    23

    Re: Units WITHOUT condensers

    Quote Originally Posted by Aiyub
    And who says Manufacturers are the "be all" and " it" who cant get it wrong

    Ive seen many ****ty products in my time, which have sold in the market place successfully.

    Because when it came to servicing the units, the poor tech had to crane his neck, stretch his limbs, and poke fiddle fart about, to get a part changed

    We still get units from reputable manufacturers without charging stubbs fitted............

    In this age of reclaim , I ask ???????
    No disagreement about any of this. It's frustrating as hell to work on a unit that was designed without regard to servicing. But most designs are a trade-off between best practices and low price. Even my own, sometimes.

    Halocarbon refrigerants were a worse idea from a refrigeration engineeering standpoint, but they were designed for safety, not efficiency. No more flooded evaporators, and oil return problems, metering problems, floodback problems, etc.

    I just thought you were annoyed because you found the embedded coil units "stupid". It just makes the entire wall one huge fin. (Technically, "secondary heat transfer surface"). Kind of clever, actually. Just a design decision, with good and bad possibilities, like all designs.

    Rog

  19. #19
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Units WITHOUT condensers

    if you don't use points in your sentences then they're very difficult to read especially for those not english spoken among us if you had read read the whole thread then you should have seen that they never said that it can work without a condensor they only said that they didn't saw a condensor those who said condensorless subscribed it between quotes """""""""""""""""""""""""""
    those who posted are good techs have a look in their older posts verify yourself was this easy to read question mark
    it's always easy to have critic this isn't alt.hvac at all had a look in your older posts (6) and all had the same negative undertone regarding to you avtar, you're kneeless and the grass need to be mowed sorry but that's my opinion
    Last edited by Peter_1; 16-11-2004 at 08:38 PM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  20. #20
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Units WITHOUT condensers

    Thanks for the back up peter, am i short of a pair of x-ray specs in my tool kit, how else was i meant to see a condenser inside a unit that i have never worked on before.

    Unlike some people who know everything !!!!!!!!!!!!!!!!!!!!!!!, i do ask what may seem stupid questions to some of the more experienced engineers, but i am no too proud to ask for help is there is something i don't know.

    Maybe one day too i will be perfect and move to aus

    Regards

    Fatboy !!!

  21. #21
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Units WITHOUT condensers

    LOL
    Or stick you nose somewhere between like VALVE750. (long time not seen...)
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  22. #22
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Units WITHOUT condensers

    Quote Originally Posted by coolkev
    u r all joking or cowboys or plane stupid how can a ref system work without a cond u must have failed physics u no change of state ect Domestic units have had condensers in the cab walls for 30 yrs that i know of . Makes me wonder if half these people should go near refs? Did they do real apprenticeships or those mail order courses?

    so were cowboys or stupid huh????
    As Peter1 says in his sig.................opening your mouth was possibly the worst thing you could have done...........
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

  23. #23
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Units WITHOUT condensers

    Quote Originally Posted by rdocwra
    Unlike some people who know everything !!!!!!!!!!!!!!!!!!!!!!!, i do ask what may seem stupid questions to some of the more experienced engineers, but i am no too proud to ask for help is there is something i don't know.

    Maybe one day too i will be perfect and move to aus

    Regards

    Fatboy !!!

    Long may you ask questions.............dont let a thick lensed spectacle boy ruffle your feathers when he should be mowing the grass instead...........
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

  24. #24
    rbartlett's Avatar
    rbartlett Guest

    Re: Units WITHOUT condensers

    Quote Originally Posted by Aiyub
    15 years ago they worked just fine..............After global warming............we have a whole new scenario here.

    Im referring to the UK..........I cant speak for your neck of the woods.

    Temperatures are much higher here now then was the case, hence the necessity for greater dissipation of heat. With coil embeddded in cabinet, not very practical now.
    sorry abe can't let you get away with this nonsense

    even the hadley data shows a 'rise' of less than one degree from the 'norm' -which in itself is a distorted figure..

    the problem of 'global warming' is more of localised heating.

    If you had said that 'England has a far denser population (not a far larger) due to urbanisation and hence the 'cities' seem to be far warmer than they used to be then I would have to agree


    cheers

    richard
    Attached Images Attached Images

  25. #25
    Join Date
    Oct 2004
    Location
    Australia
    Age
    64
    Posts
    41
    Rep Power
    0

    Thumbs up Re: Units WITHOUT condensers

    Sorry chaps. I am not a crim that was a bit low

Similar Threads

  1. What units you'll see in your country?
    By nova in forum Transport
    Replies: 25
    Last Post: 07-11-2010, 02:31 PM
  2. Mitsibishi VRV System 8 out of 10 units work
    By moondawn in forum Air Conditioning
    Replies: 5
    Last Post: 29-09-2005, 11:02 PM
  3. Highcool split air con units
    By iceman007 in forum Air Conditioning
    Replies: 10
    Last Post: 31-05-2005, 12:31 PM
  4. AC units as cooling units
    By Peter_1 in forum Commercial
    Replies: 11
    Last Post: 18-03-2005, 06:42 AM
  5. Blak Condensers
    By ben chaib in forum Domestic
    Replies: 4
    Last Post: 16-03-2002, 03:31 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •