    Mcquay Chiller problem



    Hi all, new here and finding this site very interesting, heres my issue. Called to a Mcquay ALS chiller last week, not able to investigate as customer wanting get home, so retrieved fault code after a quick test run of about 1 min before faulting, noisey comp, sounds like lubrication issue, a return visit booked in. No manual on site and Mcquay not that helpful, i could do with obtaining manual etc as much info as possible or even help on the fault.
    The circuit 2 show "NO LIQUID RUN" ?
    what does this mean, what checks can be carried out to determine the problem, any help woul be much appreciated.
    Cheers, keep up the good work.



  2. #2
    Join Date
    Sep 2007
    Location
    UK
    Age
    60
    Posts
    45
    Rep Power
    0

    Re: Mcquay Chiller problem

    The ALS chiller has probably got frame 2 Hall Screw compressors fitted, the oil charge is calculated upon the amount of refrigerant charge and is pumped into the refrigerant circuit while running. the No Liquid Run is caused due to either a faulty opto sensor which is located in the compressor body at low level or lack of refrigerant liquid injection into the machine, is there a solenoid in the liquid injection line?

    Pavilion.

  3. #3
    Join Date
    Aug 2009
    Location
    UK
    Posts
    18
    Rep Power
    0

    Re: Mcquay Chiller problem

    Quote Originally Posted by pavilion View Post
    The ALS chiller has probably got frame 2 Hall Screw compressors fitted, the oil charge is calculated upon the amount of refrigerant charge and is pumped into the refrigerant circuit while running. the No Liquid Run is caused due to either a faulty opto sensor which is located in the compressor body at low level or lack of refrigerant liquid injection into the machine, is there a solenoid in the liquid injection line?

    Pavilion.
    Yes, there is a solenoid ion the liquid injection which tested ok, put it down to lack of refrigerant due to a restricted drier.
    Going back soon with new core, will let you know.
    cheers

Similar Threads

  1. Mcquay Chiller problem
    By hitmanzak in forum Trouble Shooting
    Replies: 31
    Last Post: 24-11-2010, 04:39 PM
  2. Problem with Trane RTAD100 chiller.
    By on4hf in forum Trouble Shooting
    Replies: 8
    Last Post: 14-10-2009, 09:01 PM
  3. McQuay Chiller Wiring
    By techni in forum Air Conditioning
    Replies: 7
    Last Post: 13-10-2009, 06:23 PM
  4. Trane CVHE 450 R11 Centrifugal Chiller
    By albertjoseph in forum Air Conditioning
    Replies: 4
    Last Post: 06-10-2008, 03:23 PM
  5. York YK Chiller Problem
    By icebox in forum Refrigeration Books
    Replies: 13
    Last Post: 01-07-2008, 06:05 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •