    Clogged Cap Tube



    I think I have a clogged cap tube. I have low head pressure and low pressure is in suction. If so how hard and what is the easiest way to replace. I have not do one before. Any help would be greatful.
    Thanks Wade



  2. #2
    Join Date
    Jul 2009
    Location
    Berkshire
    Age
    50
    Posts
    175
    Rep Power
    15

    Re: Clogged Cap Tube

    Quote Originally Posted by humblepie View Post
    I think I have a clogged cap tube. I have low head pressure and low pressure is in suction. If so how hard and what is the easiest way to replace. I have not do one before. Any help would be greatful.
    Thanks Wade
    The capillary tube would generally have a strainer before it in the pipework. It's not always that obvious as it's not necessarily a "bulge point" on the pipework. The easiest is to un-braze the capillary and blow through to see if it is clogged. You may have to cut a bit of the pipework before the capillary out to clean the strainer off, which is more likely the problem.

    Incidentally, if you have low head pressure and low suction pressure, aren't you just short on refrigerant? Capillary systems are charged based on superheat, so what is your superheat value? I'm sure the clever boys will correct me, but I think you would have a high subcooling value as you back liquid up into the condenser if the capillary is blocked.

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Clogged Cap Tube

    Which refrigerant?
    What kind of machine?

    More details will help us to help you.

  4. #4
    Join Date
    Apr 2009
    Location
    WI USA
    Posts
    27
    Rep Power
    0

    Arrow Re: Clogged Cap Tube

    Quote Originally Posted by humblepie View Post
    I think I have a clogged cap tube. I have low head pressure and low suction pressure. If so how hard and what is the easiest way to replace. I have not done one before. Any help would be greatful.
    Thanks Wade
    What was the superheat & Subcooling temps? In F for me, in USA.

    Suction & head pressures, both LOW:

    SH 'High', low charge or possible restriction; SH 'Low', insufficient airflow or heatload through the cooling coil.

    We, & you, both need a lot more test data. - udarrell

Similar Threads

  1. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 01:03 PM
  2. Cap Tube Design Program - Results
    By Chef in forum Fundamentals
    Replies: 3
    Last Post: 01-09-2008, 09:49 AM
  3. excess tube length on condenser tube plate
    By onquin in forum Fundamentals
    Replies: 4
    Last Post: 15-11-2007, 06:03 AM
  4. Coils - Inline vs Staggered tube
    By nh3simman in forum Fundamentals
    Replies: 15
    Last Post: 03-04-2007, 08:25 PM
  5. metric capillary tube
    By tralex in forum Fundamentals
    Replies: 5
    Last Post: 21-02-2006, 06:57 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •