    kwhr versus deg celsius



    Hello,
    New to this site and forum, but can anyone help me please.

    How much energy (in kwhr) will I need to change 1 deg celsius (up or down) from any refererence temperature and any reference room size.

    say: the room size is w=6m, l=5m, h=2.5m initial room temperature 24deg celsius, wall concrete plaster, outside temp 31deg celsius; question= how much kwhr will I need to reduce or increase the room temperature by 1 deg celsius.



  2. #2
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: kwhr versus deg celsius

    Hi Mr. Trichocereus Pachanoi MP
    You would not require any kWhr to increase the temp as it will do this naturally. How thick is the wall and we must assume you would like to do this in 1 hour? Should we also assume you will be starting at 50%RH with no windows or air infiltration?

  3. #3
    sanpedromp's Avatar
    sanpedromp Guest

    Re: kwhr versus deg celsius

    Hello Tesla, thanks for the reply, but I am sure you are missing the point, my question was "How much energy (in kwhr) will I need to change 1 deg celsius (up or down) from any refererence temperature and any reference room size." and with the following assumptions on the next paragraph.

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: kwhr versus deg celsius

    You need to know u value of your walls (floor,ceiling, window etc....) . Than you should calculate overall heat transfer by multiplying each wall (floor,ceiling, window etc....) area with corresponding u value of that part and than sum all that. Since u value is given by kW/m^2K, you got your heat/cool energy for change of 1°C.
    Last edited by nike123; 19-08-2009 at 02:24 PM.

Similar Threads

  1. Replies: 11
    Last Post: 06-01-2011, 03:35 AM
  2. converting a calculation to Si
    By marc5180 in forum Fundamentals
    Replies: 14
    Last Post: 10-05-2009, 09:41 PM
  3. Replies: 6
    Last Post: 27-11-2008, 09:52 AM
  4. LG versus Hitachi ..... your opinions please
    By Ireland in forum Air Conditioning
    Replies: 8
    Last Post: 13-07-2007, 06:49 PM
  5. Hermetic reciprocating versus hermetic scroll
    By Cofreth in forum Technical Discussions
    Replies: 26
    Last Post: 19-11-2005, 06:29 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •