Thread: kwhr versus deg celsius
-
18-08-2009, 10:15 AM #1
kwhr versus deg celsius
Hello,
New to this site and forum, but can anyone help me please.
How much energy (in kwhr) will I need to change 1 deg celsius (up or down) from any refererence temperature and any reference room size.
say: the room size is w=6m, l=5m, h=2.5m initial room temperature 24deg celsius, wall concrete plaster, outside temp 31deg celsius; question= how much kwhr will I need to reduce or increase the room temperature by 1 deg celsius.
-
18-08-2009, 02:37 PM #2
Re: kwhr versus deg celsius
Hi Mr. Trichocereus Pachanoi MP
You would not require any kWhr to increase the temp as it will do this naturally. How thick is the wall and we must assume you would like to do this in 1 hour? Should we also assume you will be starting at 50%RH with no windows or air infiltration?
-
19-08-2009, 10:09 AM #3
Re: kwhr versus deg celsius
Hello Tesla, thanks for the reply, but I am sure you are missing the point, my question was "How much energy (in kwhr) will I need to change 1 deg celsius (up or down) from any refererence temperature and any reference room size." and with the following assumptions on the next paragraph.
-
19-08-2009, 02:13 PM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: kwhr versus deg celsius
You need to know u value of your walls (floor,ceiling, window etc....) . Than you should calculate overall heat transfer by multiplying each wall (floor,ceiling, window etc....) area with corresponding u value of that part and than sum all that. Since u value is given by kW/m^2K, you got your heat/cool energy for change of 1°C.
Last edited by nike123; 19-08-2009 at 02:24 PM.
Similar Threads
-
screw compressor versus Reciprocating compreesor in refrigearion.
By patilvasudeo in forum FundamentalsReplies: 11Last Post: 06-01-2011, 03:35 AM -
converting a calculation to Si
By marc5180 in forum FundamentalsReplies: 14Last Post: 10-05-2009, 09:41 PM -
Comparison sheet 10 ton air cooled chiller versus vrf versus conventional split
By abbasi in forum FundamentalsReplies: 6Last Post: 27-11-2008, 09:52 AM -
LG versus Hitachi ..... your opinions please
By Ireland in forum Air ConditioningReplies: 8Last Post: 13-07-2007, 06:49 PM -
Hermetic reciprocating versus hermetic scroll
By Cofreth in forum Technical DiscussionsReplies: 26Last Post: 19-11-2005, 06:29 PM