    Refrigerant Falsification



    In my country many that forged the cooling material with only replaced the package.
    The example R12 in the tube R134A.
    that wanted to be asked about by me, was how distinguished between R12 and R134A?



  2. #2
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Refrigerant Falsification

    I dont believe it is possible to at once discerne a forgery - without special instruments (some spectrographs or alike) at least - the falcifiers are probably carefull enough as to make such mixtures which by their pressure to temperature characteristics will be identical to the refrigerants falcified.

    Everything is being falcified in the world - from jewels to medicines to fuel. Buy your refrigerants only from people who are licenced providers and, maybe, interrogate about their licence by your Refrigeration Engineers Association.

  3. #3
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Refrigerant Falsification

    I have come across Chinese-manufactured R-134a, that responded totally differently, in a test machine, to the correct brand-name refrigerant.

    Tests at various points in the refrigeration circuit will show up the performance differences - they are impossible to imitate perfectly.

    Don't buy Chinese copies.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  4. #4
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: Refrigerant Falsification

    Could one not do a standing pressure/temperature test at various temperatures to determine these refrigerants and compare to a pressure temperature chart?

  5. #5
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Refrigerant Falsification

    Take a few system readings, together with the standard sat pressure/temp for the original gas, then for the 'supadupa goop' from the supplier of choice.

    If the mass charge is identical, & the system performs differently, then you will know.

    Dupont wrote an article about some of the junk refrigerants sold in Dubai - origin Asia. The findings were scary, to say the very least. Some of the stuff was flammable... go figure what's in there.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  6. #6
    Join Date
    Nov 2008
    Location
    Indonesia
    Age
    50
    Posts
    27
    Rep Power
    0

    Re: Refrigerant Falsification

    I really hope for very much from the holder's side of the make licence dupont to check his product, possibly also was forged in my country.

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  3. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  4. MHI FDCA400HKXRE4 Tech Info Please
    By L.JT in forum Trouble Shooting
    Replies: 5
    Last Post: 23-08-2008, 11:00 PM
  5. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •