    Charging with a restricted condenser



    I will be going to repair a unit ( cracked discharge piping due to broken compressor mount ) I have been told that the ambient airflow to the condenser is somewhat restricted and that because of an I beam about 2.5m in font of the condenser the air leaving the coil shortcyles back onto itself.

    After the repairs to mounting and pipe, leak check, drier core change and vacuum. I need to charge the unit. If I charge to a subcooling of between 4 & 7 deg C, I am expecting that I will have slightly higher than normal HP and a still flashing sightglass.

    Any help or thoughts on the matter will be appreciated.

    frank14



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Charging with a restricted condenser

    Move the condenser. Recirculating the air will increase the operating cost and shorten the lifespan of the system.

  3. #3
    Join Date
    May 2008
    Location
    Port Elizabeth SA
    Posts
    21
    Rep Power
    0

    Re: Charging with a restricted condenser

    Gary

    That is the first thing I suggested.

    Its on a drilling rig.

    1. there really is not anywhere else
    2. the on board guys would battle to justfy the time and cost to move it if there was a more suitable place, but would have no problem to replace the unit every couple of years.

    Looking forward to your wisdom as to charging the unit

    Thanks

    Frank14

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Charging with a restricted condenser

    In that case, the system is better off with minimum subcooling. If there is enough refrigerant to feed the coil (proper superheat), then it doesn't matter if the sightglass flashes and the HP won't run quite as high. A slight undercharge is the lesser of evils.
    Last edited by Gary; 15-08-2009 at 11:06 AM.

  5. #5
    Join Date
    May 2008
    Location
    Port Elizabeth SA
    Posts
    21
    Rep Power
    0

    Re: Charging with a restricted condenser

    Gary

    Thanks again for the wisdom

    frank14

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Charging with a restricted condenser

    I should monitor both (SH especially and SC) : if SH drops while filling to 7 /10 K and SC is then only 1 or 2K, then I should leave it this way.
    Can't you install some sort of deflector before the beam so that the air is more guided?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. High discharge temp
    By paul_h in forum Air Conditioning
    Replies: 48
    Last Post: 06-05-2009, 11:10 AM
  3. Air Cooled Condenser Leakage Problem with R-404A
    By RADHAKRISHNARAO in forum Technical Discussions
    Replies: 19
    Last Post: 30-07-2008, 12:21 PM
  4. Plate Heat Exchagers - Condenser
    By Billy Ray in forum Technical Discussions
    Replies: 9
    Last Post: 11-05-2008, 06:16 PM
  5. Optimum condenser fan speed
    By star882 in forum Fundamentals
    Replies: 4
    Last Post: 27-02-2006, 01:50 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •