15-08-2009, 04:26 AM #1
Charging with a restricted condenser
I will be going to repair a unit ( cracked discharge piping due to broken compressor mount ) I have been told that the ambient airflow to the condenser is somewhat restricted and that because of an I beam about 2.5m in font of the condenser the air leaving the coil shortcyles back onto itself.
After the repairs to mounting and pipe, leak check, drier core change and vacuum. I need to charge the unit. If I charge to a subcooling of between 4 & 7 deg C, I am expecting that I will have slightly higher than normal HP and a still flashing sightglass.
Any help or thoughts on the matter will be appreciated.
frank14
15-08-2009, 04:36 AM #2
Re: Charging with a restricted condenser
Move the condenser. Recirculating the air will increase the operating cost and shorten the lifespan of the system.
15-08-2009, 09:47 AM #3
Gary
That is the first thing I suggested.
Its on a drilling rig.
1. there really is not anywhere else
2. the on board guys would battle to justfy the time and cost to move it if there was a more suitable place, but would have no problem to replace the unit every couple of years.
Looking forward to your wisdom as to charging the unit
Frank14
15-08-2009, 10:59 AM #4
In that case, the system is better off with minimum subcooling. If there is enough refrigerant to feed the coil (proper superheat), then it doesn't matter if the sightglass flashes and the HP won't run quite as high. A slight undercharge is the lesser of evils.
16-08-2009, 04:13 AM #5
Gary
Thanks again for the wisdom
frank14
16-08-2009, 07:39 AM #6
I should monitor both (SH especially and SC) : if SH drops while filling to 7 /10 K and SC is then only 1 or 2K, then I should leave it this way.
Can't you install some sort of deflector before the beam so that the air is more guided?It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
High discharge temp
By paul_h in forum Air ConditioningReplies: 48Last Post: 06-05-2009, 11:10 AM -
Air Cooled Condenser Leakage Problem with R-404A
By RADHAKRISHNARAO in forum Technical DiscussionsReplies: 19Last Post: 30-07-2008, 12:21 PM -
Plate Heat Exchagers - Condenser
By Billy Ray in forum Technical DiscussionsReplies: 9Last Post: 11-05-2008, 06:16 PM -
Optimum condenser fan speed
By star882 in forum FundamentalsReplies: 4Last Post: 27-02-2006, 01:50 AM