    Email air - dn186h



    hi all,

    ive got an email air - dn186h aircon which isnt heating. reading the error codes, the red light is flashing fast, green flashing slowly, and the error states this : F, C & H are 24v input signals

    Can someone please let me know what that may mean, and possibly how i could resolve this issue??

    Also if anyone has any web links or docs on how best to troubleshoot these particular units, would be greatly appreciated.

    Cheers



  2. #2
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Email air - dn186h

    G'day.

    It should have a sticker or it will be written somewhere on the unit what the error codes are, unless someone has removed it.

    Heatcraft can supply spares for that unit, try them they may be able to help.

  3. #3
    Join Date
    Aug 2009
    Location
    Sydney
    Posts
    6
    Rep Power
    0

    Re: Email air - dn186h

    thanks for the prompt reply temprite..

    yeah looking at the sticker, the only answer to the error code on the sticker is:

    F, C & H are 24v input signals

    doesnt tell me anything else..

  4. #4
    Join Date
    Oct 2008
    Location
    Australia
    Posts
    210
    Rep Power
    16

    Re: Email air - dn186h

    im pretty sure those units only fault out on safety circuit faults. so just loop out the safety circuits and see if the units starts.

    The F C and H are only what the controller is sending to the condensing unit, so from what i can tell is its calling for fan, compressor and heat. So the board is getting its inputs but not sending out any outputs.

    Also just a guess the board could be blown. But try the safety circuit 1st.

  5. #5
    Join Date
    Aug 2009
    Location
    Sydney
    Posts
    6
    Rep Power
    0

    Re: Email air - dn186h

    thanks rude,

    that hasnt really helped either. not sure what else to try

Similar Threads

  1. Old email DN186H
    By paul_h in forum Air Conditioning
    Replies: 21
    Last Post: 28-09-2009, 02:29 AM
  2. New email details. RE. Grizzly
    By Grizzly in forum New to RE
    Replies: 1
    Last Post: 24-01-2009, 08:41 PM
  3. Email weatherwall charge quantity?
    By Actinide in forum Air Conditioning
    Replies: 1
    Last Post: 18-12-2006, 11:07 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •